Bastian_Schmitz
Bastian_Schmitz Champion
38
LeTomas
LeTomas Mentor
14
ismailozinan
ismailozinan Leader
8
EcoStruxureโ„ข Machine Expert - HVAC
Caroko_Tri_Hatmojo
Caroko_Tri_Hatmojo
Explorer
Posted: โ€Ž2022-08-26 09:00 PM
4
4075
Hi I want ask question about PLC TM172PBG28R, I use Ecostructure Machine Expert - HVAC to program this PLC. I already made Running Machine with hours and minute accuracy, but I have a problem saving run hours and run minutes in EEPROM. When a flicker occurs, the EEPROM hours storage section is reset to 0. Is there any other solution how to save EEPROM which is better?
Here I attach a screenshot of the PLC program that I have made
fbd run pointer to EEPROMfbd run pointer to EEPROMRst and condition Run HoursRst and condition Run Hours
Best Regards
Caroko Tri (Electrical Engineer in PT. Infion Pharma Indonesia)
  • eeprom
  • memory
  • plc
  • TM172
Bastian_Schmitz
Champion
Posted: โ€Ž2022-08-29 01:01 AM
In response to Caroko_Tri_Hatmojo
4019
You did not have the possiblity to do anything if the power get cut off.
But you can notice a power on, but not a power off.
The problem is that you write directly on the EEPROM. And the EEPROM is specified "only" for 100.000 writes. If you increse these number of writes the memory could be destroyed. The value will always stored in EEPROM. If you store everything on the SD card this will so far I know not solve this issue.
If you write on the EEPROM if a Anlog Value changes you will destroy the memory of the controler.
Replies 4
Bastian_Schmitz
Champion
Posted: โ€Ž2022-08-29 12:10 AM
4028
Please consider that you prevent to reach more then 100.000 writes on eeprom values. Otherwise you would destroy the memory. I could not see with which frequency you use "sysWritePar****".
Regarding to this the use of a hour counter with minute resolution is not recommend.
Generell the writing to eeprom seems to be correct so far ud_Run_hours and ud_Run_Minutes representing the EEPROM values.
I would suggest maybe a missing initalistation of the values of ud_operating_Minutes and ud_Operating are the problem.
Did you mean with flicker a restart of the machine? (Power On/Off)
Caroko_Tri_Hatmojo
Caroko_Tri_Hatmojo
Explorer
Posted: โ€Ž2022-08-29 12:47 AM
In response to Bastian_Schmitz
4023
Thank you for your answer @Bastian_Schmitz . I Use SD Card on my PLC, so *.PAR file will save in my SD Card, does it still affect EEPROM?
Did you mean frequency is Task Configuration? If yes, I use 100 ms
Task ConfigurationTask Configuration
Yes flicker means Power On/Off.  At my factory often occurs flicker. So I need non-volatile storage to save running hours. I want to make the program work like this, when flicker occurs (PLC OFF) my Operating Hours (format hours and minutes) save to EEPROM (ud_Hours & ud_Minutes) and when PLC is ON, value EEPROM transfer to volatile memory (ud_Operating_minutes & ud_Operating), so calculation of operating hours (format hours and minutes) can be continued.
I use DPT (Differential Pressure Transmitter) feedback to indicate my machine flicker. See my program (Rst_Running_Hours), on 'AI_DPT'. So when DPT is low value EEPROM transfer to volatile memory (ud_Operating_minutes & ud_Operating).
  • eeprom
  • Running Hours
  • TM172 PLC
Bastian_Schmitz
Champion
4020
Caroko_Tri_Hatmojo
Caroko_Tri_Hatmojo
Explorer
Posted: โ€Ž2022-08-29 01:11 AM
Thank you @Bastian_Schmitz your answer really helped me ๐Ÿ™‚
ย
WHATโ€™S NEXT?
Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric