Posted: 2022-08-05 06:59 AM
Do we have a replacement for the discontinued fast acting fuses?
If no replacement, does it mean that we don't need the fuses for type 2 co-ordination?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-18 06:24 AM
The type 2 coordination means it is not necessary to replace any internal component of internal Soft Starter in case of huge damage on motor side (meaning short circuit). In such a case of Short circuit, it is tolerated to check the line contactor (could be light welded but shall be open using a screwdriver) and the fast fuse will protect the internal power components of the Soft Starter (Thyristors).
You can see a table giving fast acting fuses necessary on ATS48 for type 2 coordination.