Vijeo Designer 6.3 and Harmony P6
Dear all,
Due to obsolescence we have to move from iPC HMIPSPS752D1801 to Harmony P6.
Using version 6.3, the Vijeo Designer application looks 100% compatible and we are happy with it.
But until now we are unable to install the “vda” file on the target.
Also, also, using USB cable for download (From VJD 6.3 to P6) there is a message which says that target is not recognized.
Is there a specific run time software for Harmony P6?
(it looks that licence is different)
If yes, where to get it?
If no, any idea about this issue?
I hope you can help.
- Labels:
-
Process Automation Talks
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-09 02:08 AM
Hi, There is an Vijeo Designer Runtime reference espacially for P6 available
VJDRTPROH1P
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-09 11:17 PM
Hi,
Thanks for your comment.
Yes this is the reference of the License for 6.3.
Update:
Application built with 6.2 sp12 and run time installed (*) on target: It works
Application (Same) built with 6.3 and run time installed (*) on target: It does not work.
(*) trial period
Still digging...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-26 04:21 PM . Last Modified: 2025-02-26 04:23 PM
Anyone got this fixed. I can't get mine out of trial mode. My activation is specifically for the P6 with runtime. Im running 6.2 sp12 and it's stuck in trial mode. Anyone know how to fix?
Does the runtime have to be specific? Not just 6.2 sp12 but also one specific for the P6?? I know the activation is specific for the p6 and I'm good there but stuck in trial mode. I've got FAT in two weeks if anyone can give an idea