Unity Pro / Control Expert: How to 'suppress' arithmetic overflow diagnostic entry via logic

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Unity Pro / Control Expert: How to 'suppress' arithmetic overflow diagnostic entry via logic
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-25 04:59 PM

0 Likes
5
5420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-25 04:59 PM

Unity Pro / Control Expert: How to 'suppress' arithmetic overflow diagnostic entry via logic

Hi,

 

I have a piece of code that is used for a linear congruential psuedo-random number generator, however one of the arithmetic operations deliberately overflows.  I know that this will happen, it's entirely expected behaviour, and I don't wish to have additional code that will alter this behaviour (since this existing code has already been characterised, and I don't wish to revisit this).

 

How would I go about disabling the diagnostic reporting of this particular arithmetic overflow however?

I was expecting that there would be an EF that could be called prior to the operation, passing in a mask of arithmetic errors, and then I could call the same EF afterwards to restore the previous mask.

 

Has anyone done something similar?

 

It becomes quite an issue that the fault light comes on, and requires someone to access the controller and acknowledge this 'fault'.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Labels
  • Labels:
  • Smart Design & Engineering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Alpenglow
Ensign Alpenglow
Ensign

Posted: ‎2020-06-25 05:15 PM . Last Modified: ‎2020-06-25 05:16 PM

1 Like
4
5414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-25 05:15 PM . Last Modified: ‎2020-06-25 05:16 PM

If you look at Help you'll see that %S18 directly addresses our overflow error.  However, if you read towards the bottom you'll see the following:

 

"When the %S18 bit switches to 1, the application stops in error state if the %S78 bit has been set to 1". 

 

%S78 is the "halt if error" occurs.  You could try writing a 0 to %S78 so that if the error occurs (i.e. overflow) at %S18 then it won't make any difference because the conditional bit (%S78) is not set to 1.  



Blue side up.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-25 05:47 PM

In response to Alpenglow
0 Likes
3
5409
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-25 05:47 PM

%S78 doesn't stop the 'error' from being entered in the Diagnostics Logs, and flashing the fault light.

It just changes whether that results in the process HALTing also.

 

I do NOT have %S78 set, so the HALT isn't my problem.  The diagnostic entry, and fault light behaviour is.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Alpenglow
Ensign Alpenglow
Ensign

Posted: ‎2020-06-25 05:56 PM

In response to BevanWeiss
1 Like
2
5403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-25 05:56 PM

Yes you are correct.  Perhaps I misunderstood. 

 

I do not know of any method to prevent such an error occurring. 

 

 

All the best. 



Blue side up.
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Eric_Coudurier
Lt. Commander Eric_Coudurier Lt. Commander
Lt. Commander

Posted: ‎2020-06-26 02:34 PM

In response to Alpenglow
1 Like
1
5374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-26 02:34 PM

There is no way to prevent the overflow error, but you can just reset the overflow bit after the execution of your function. Or prevent the execution of the function if it will lead to an overflow. The system diagnostic can be disabled if you don’t want to log this kind of errors.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-06-26 09:07 PM

In response to Eric_Coudurier
0 Likes
0
5369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-26 09:07 PM

Thanks @Eric_Coudurier,

So if I was doing this:

PrevSW125 := %SW125;
PrevS18 := %S18;
cong := 69069*cong+1234567;
%SW125 := PrevSW125;
%S18 := PrevS18;

 

What is expected to be 'different'.. it appears to still generate the system diagnostic log entry, and I suspect that it will still flash the fault light.

 

I really don't want to just turn off the system diagnostics, since it's incredibly useful for other situations, like genuine code errors (e.g. index array out of bounds, PIDIFF instructions with inf/sup set to the same values etc).

 

Unfortunately the overflow is a part of the operation.  A MODulus could be performed.. but it's already using a UDINT, so there's no bigger elementary type that I could use to fit the operation and then MOD it back down (right?)

 

Converting to a REAL for the dynamic range will ruin the entire psuedo-random behaviour of it (NOTE: I'm not using this for cryptography, so the trivial prediction of the sequence is not an issue... but the 'random' distribution of results is necessary)

 


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore