Guys, is it correct to set the IP address like this to synchronize the time of your SCADA system?
I want to synchronize the time of the Scada system using the NTP protocol.sync.jpg
  • Cybersecurity
  • Edge Control
  • Smart Operations
  • Training
dmah
Crewman dmah Crewman
Crewman
Posted: ‎2025-07-28 07:53 AM
Should be okay. If you're not getting any response, check:
- Can you ping the NTP server?
- Is there a route from your machine to the NTP server?
- Is there a firewall clocking traffic to the NTP server or the port 123?
If you have access to PowerShell, you can run the command:
Test-NetConnection -Computer 10.10.18.254 -Port 123