Support regarding PLC M580 over the network
  • Industrial Automation
  • Support regarding PLC M580 over the network
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
anupky1979
Crewman anupky1979
Crewman
Posted: ‎2025-06-18 11:14 PM
2503
Dear Team,
We want your support for the PLC M580, over the network.
Also 1) please tell us if we can have the possibility of removing the broadcasts from the PLC, which are of no use.
        2) and is there any possibility of having two IP ranges in the PLC M580?
Please reply as soon as possible
Replies 9
Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant
Posted: ‎2025-06-24 09:13 PM
2456
Not sure which broadcasts you refer to. As for your 2nd question, you can use BMXNOC0321 with port forwarding with 2 ip subnets to segregate your device and control networks.
BR
JerryBartlemay
Lieutenant JG
Posted: ‎2025-06-25 07:54 AM
1
2443
Broadcasts such as BootP, DHCP and ARP are part of the address server.  The service port of the CPU is part of the EIO system, and even though it doesn't support EIO drops directly, it does support the address server.  If you connect the service port of the CPU to the plant network, these messages will be sent out.
Because these messages are now on the plant network, this means you are cross connecting EIO systems on multiple M580s, never a good thing.  Hennie is spot on; using the BMXNOC0321 will isolate the EIO system, not sending its broadcast messages, and give you multiple IP subnet support.  I've attached my white paper on M580 architectures that addresses these questions.
anupky1979
Crewman anupky1979
Crewman
Posted: ‎2025-06-26 02:18 AM
Hello All,
We are facing some instability issues in the network setup shown below, where one of the devices PQ meter keeps disconnecting intermittently and reconnects after a short while. This behavior then repeats periodically.
The network looks like below -
Our Observations and Queries-
1. Excessive Broadcasts in the Network
Upon analyzing the network traffic using Wireshark (via port mirroring on the Advantech switch), we observed a significant number of broadcast packets being sent across the network.
  • Many of these broadcasts appear to be unnecessary for the PQ meter.
  • Below is a snapshot from the PCAP file showing a few IP addresses that are generating broadcast traffic very frequently (though there are others as well):
Our Request:
Is there a way to suppress or disable unnecessary broadcast traffic from the PLC M580, particularly if it's not essential for device communication?
We suspect this excess broadcast traffic could be impacting the stability of the PQ meter’s connection.
2) Network Segmentation via VLAN
To further isolate and stabilize the PQ meter's communication path:
Query:
Does the PLC M580 support dual IP addressing or VLAN configuration?
If so, can we configure two IP ranges one for general PLC communication and another isolated VLAN specifically for the PQ meter to avoid interference?
In total that is what needs to establish, PQ meter connected well to PLC M580, so that it never disconnects due to any setting from PLC.
anupky1979
Crewman anupky1979
Crewman
Posted: ‎2025-06-26 04:19 AM
In response to JerryBartlemay
I have updated the whole scenario, please have a look into it and let me know what i can do about it.
anupky1979
Crewman anupky1979
Crewman
Posted: ‎2025-06-26 08:56 PM
In response to Hennie_Smith
I have elaborated the issue, please have a look and let me know what to proceed with.
Hennie_Smith
Lieutenant
Posted: ‎2025-06-26 10:26 PM
3
2393
The M580 cannot be configured with Vlan. We still need bit more information.
  1. What protocol are you using to communicate to the PQ meter?
  2. Does the PQ meter support EthernetIP or DNP3?
  3. In your trace, could you provide the IP addresses for the equipment mentioned? The PLC in particular try to establish communication to a number of different IP's unsuccessfully on Layer 2 which causes the ARP messages.
  4. Are you communicating from the PLC via a NOC card or from the CPU port? Can you capture a trace with the service port of the NOC/CPU set as mirror port?Hennie_Smith_0-1751001406787.png
If you want to isolate the comms to the PQ from other communication you would need to have a dedicated NOC301 card with separate connection to the switch. The Advantech switch need to be configured to Vlan tag all communication from the PLC on that port. You would need additional managed switch before the PQ meter to untag the vlan if the meter does not support vlan configuration itself.
Hennie
anupky1979
Crewman anupky1979
Crewman
Posted: ‎2025-06-29 11:32 PM
2304
Hello Hennie,
Thank you so much for supporting and helping us.
Please find the answers below to your respective questions-
1) Modbus TCP/IP
2) Th PQ meter does Support the Ethernet. Manual is attached.
3) The IP of the PQ meter is 172.16.0.42.
                          Primary PLC- 172.16.0.33
                          Secondary PLC is 172.16.0.34
                          Primary PLC Switch is 172.16.0.39
I have attached an excel sheet of list of IP addresses that are used on network.
4) Regarding the Connection to which port is done, I have attached a photo of PLC and a video of the Panel, explaining in short. and about rest of the things you have mentioned about , can you please guide a little more about it ? we will definitely implement what you would recommend to solve this issue, moreover also can you please let me know that after implementing those settings in the existing network what you suggest for, can the problem be finished?
Also I Received a larger view the existing architecture, I have attached it.
Additionally, Please let me know if we can communicate on mail, that way it would be faster and more efficient.
Hennie_Smith
Lieutenant
Posted: ‎2025-06-30 12:39 AM
In response to anupky1979
Good day,
I sent you email which we can discuss the issue further.
Hennie
JerryBartlemay
Lieutenant JG
Posted: ‎2025-07-01 07:56 AM
I see that the NOC module is in the same IP subnet as the processor.  Provided the backplane Ethernet port of the NOC is not enabled (disabled is the default), simply moving the network connection from the service port of the processor to the NOC would isolate the EIO system from the network and block the broadcasts coming from that source.