HI ALL
I started a thread earlier about my SCADAPack 535E rPAC losing configuration and
had great discussion with @BevanWeiss ,
Now I had to start new thread as this is really weird and very confusing , Sometimes when I reboot the RTU it would
not go RUN mode , it will start with status led off then it will go on for ten seconds , after that it will blink on and off for
about ten seconds and at last it will remain lit forever and it will not respond to any connection attempt
This scenario should happen when someone tries to cold boot or factory boot the RTU ,
The only solution is to keep the RTU powered off for a day or two
then it can be started normally
I have upgraded the firmware and boot loader for the RTU to the latest versions
firmware v 8.14.7
boot loader v 1.30
this was happening before the update and still happening after.
I thought the update would correct this issue, but it did not
thank you in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-02-28 04:56 PM
And to confirm you are NOT depressing the SELECT button at ANY time during this occurring?
What supply voltage are you powering the SP535E Controller (the top terminals) via?
Have you confirmed that the power supply has an adequate startup current capability?
I've seen several amps drawn at startup of a SP535E, so the power supply should be capable of this kind of consumption momentarily without dropping the voltage below 11.5V (12V for good measure).
Does this happen even if you DO NOT load an RTU configuration into the unit? (i.e. Factory Boot as per 10.4 of the Hardware Manual and then just leave it powered on for several days, then remove power, and re-apply) It should have DNP3 address 0, and Factory Default settings for ports.
If it still does this on a Factory Boot, then you should connect a serial port connection to Port 4, and use HyperTerminal or a similar Terminal program to observe the boot messages. It should reveal the issue.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-02-29 02:15 AM . Last Modified: โ2020-02-29 02:17 AM
Thanks @BevanWeiss
Just back from the site where the RTU located,
I carried out checks you mentioned in your last reply
1/ The SELECT push button is not pushed at any time during RTU startup
2/ Applied voltage to the RTU remains constant at 24v DC during startup , so no drop in voltage happens due to excessive amps drawn (check done twice)
I also disconnected ALL wiring and ethenet cables to the RTU just to make sure that nothing from outside affect the boot process (I know this has nothing to do with booting up)
Yes this happens even without the configuration files being loaded to the RTU
Looks like I have to try connecting to serial port through port 4 with hyper terminal
please watch this video, It was recorded 3 hours ago
Have a good day
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-02-29 04:28 AM . Last Modified: โ2020-02-29 04:31 AM
I've never seen a SP535E with the DIP switch exposed. It normally has a metal sheet still covering it.
Although I've just looked at the hardware manual and it does show the exposed upper rotary switch. So my memory must be deceiving me.
I think that you might need to contact Schneider Tech Support about getting an RMA for this unit.
If it's misbehaving after a Factory Boot then it seems like a hardware issue (from that video it seems like the SELECT pushbutton is stuck 'on').
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-02-29 09:03 AM
I appreciate your contribution @BevanWeiss
Am I still able to connect to the RTU through serial port 4 by means of Teminal software??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-02-29 06:47 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-04 05:07 AM
I have done updating with 2 RTUs
for both main firmware and 6601 I/O
when I came to third one , firmware and boot loader were OK for the RTU , but when trying update for I/O module , it looks like the RTU can not "see" the 6601 I/O modules
it says " make sure that the I/O modules are configured
and the version of the firmware of module shows 0.00.0 when refreshing the general page
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-04 04:59 PM
Configuration File Invalid. Factory Reset the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-05 12:18 AM
I did and nothing changed, actually another RTU had the same problem today,
Everything is collapsing ๐
I think I have to put back the old firmware
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-05 12:34 AM
I've never seen a 'Configuration File Invalid' error after a Factory Restart.
Only ever after having downloaded a configuration to it.
And normally you could then check the config.log file which will contain the error
If you get that error after a Factory Restart, I'd contact Schneider Tech Support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-05 01:58 AM
No configuration error showed up , but Now an other RTU also have 6601 I/O firmware set to 0.00.0
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-03-19 08:08 AM
Dear @OsamaSalih , please contact TRSS-Support@schneider-electric.com. Make sure to include as much detail as possible... and to share their solution with us, once you have it ๐
Link copied. Please paste this link to share this article on your social media post.
Youโve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.