SAITEL DP CPU866e -EB V1.7.30 - New SM_AI8AO4 - AO output not working in Voltage / Current configuration

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • SAITEL DP CPU866e -EB V1.7.30 - New SM_AI8AO4 - AO output not working in Voltage / Current configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
SESA586716
Ensign SESA586716 Ensign
Ensign

Posted: ‎2024-12-03 09:07 PM

0 Likes
3
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-03 09:07 PM

SAITEL DP CPU866e -EB V1.7.30 - New SM_AI8AO4 - AO output not working in Voltage / Current configuration

Hello Juan Rayo,

 

Hope you are doign good !!...

CPU866e - EB V1.7.30 - AI8AO4 module AO configured as Voltage (0/5V) or Current (4/20mA) but we are not getting the output in field TB.

 

As per AI8AO4 user manual It was observed that there is some jumper setting for Voltage/Current configuration, but in newly supplied AI8AO4 modules (PN- M525200002E6, SN- 2441R1511239 )internal PCB there is no Jumper settings.

 

Pictures enclosed for your quick reference. AO Wiring, AO_TB we are using at your panel pic enclosed.

New AI8AO4 PCB picture also enclosed.

 

Can you suggest How to check the AO signals?

 

Regards,

Amarnadh P

 

 

 

Attachments
Labels
  • Labels:
  • Connected Products
  • Tags:
  • english
  • Saitel DP
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2024-12-04 03:01 AM

0 Likes
0
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 03:01 AM

Definitely the document is wrong in terms of jumpers needed. The module only works with current as default BUT if you want to work with voltage you must add resistances in the fieldTB and then select the correct working voltage level depending on the resistance´s value added. We start working to correct the document, thanks for the feedback

Reply

Link copied. Please paste this link to share this article on your social media post.

JuanRayo
Lieutenant JuanRayo Lieutenant
Lieutenant

Posted: ‎2024-12-04 03:16 AM

0 Likes
0
739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 03:16 AM

I am attaching the new document for this module, different physical aspect (for PowerLogic T500) but the same functionality. Apologize for the document issue 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

SESA586716
Ensign SESA586716 Ensign
Ensign

Posted: ‎2024-12-04 07:47 AM

0 Likes
0
721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-04 07:47 AM

Thank You for your support!!

There was Hardware issue. We have replace with new one. Now it is working.

Regards,

Amarnadh p

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of