SAITEL DP CPU866e -EB V1.7.30 - New SM_AI8AO4 - AO output not working in Voltage / Current configuration
  • Industrial Automation
  • SAITEL DP CPU866e -EB V1.7.30 - New SM_AI8AO4 - AO output not working in Voltage / Current configuration
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
SESA586716
Ensign SESA586716 Ensign
Ensign
Posted: ‎2024-12-03 09:07 PM
1559
Hello Juan Rayo,
Hope you are doign good !!...
CPU866e - EB V1.7.30 - AI8AO4 module AO configured as Voltage (0/5V) or Current (4/20mA) but we are not getting the output in field TB.
As per AI8AO4 user manual It was observed that there is some jumper setting for Voltage/Current configuration, but in newly supplied AI8AO4 modules (PN- M525200002E6, SN- 2441R1511239 )internal PCB there is no Jumper settings.
Pictures enclosed for your quick reference. AO Wiring, AO_TB we are using at your panel pic enclosed.
New AI8AO4 PCB picture also enclosed.
Can you suggest How to check the AO signals?
Amarnadh P
  • Connected Products
  • Saitel DP
JuanRayo
Lt. Commander JuanRayo Lt. Commander
Lt. Commander
Posted: ‎2024-12-04 03:01 AM
Definitely the document is wrong in terms of jumpers needed. The module only works with current as default BUT if you want to work with voltage you must add resistances in the fieldTB and then select the correct working voltage level depending on the resistance´s value added. We start working to correct the document, thanks for the feedback
JuanRayo
Lt. Commander
Posted: ‎2024-12-04 03:16 AM
I am attaching the new document for this module, different physical aspect (for PowerLogic T500) but the same functionality. Apologize for the document issue
SESA586716
Ensign
Posted: ‎2024-12-04 07:47 AM
Thank You for your support!!
There was Hardware issue. We have replace with new one. Now it is working.
Amarnadh p