Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Posted: 2020-04-29 11:04 AM . Last Modified: 2021-06-03 07:51 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-29 11:04 AM . Last Modified: 2021-06-03 07:51 AM
Now we are proposed 244LD LevelStar model: 244LD-SS3R2RNNH1C4-ML124 for High Pressure Steam drum application to replace the existing Level Switch old design.
Process condition is very hot environment as below;
-Pressure = 94.8 kscg
-Temperature = 306 C
-Ambient temp is 100 DegC
Right now customer concern about ambient temp is 100DegC will be make our 244LD transmitter to failure in short time.
Now they are request 244LD with remote mounting and please support this request.
Note: 244LD with Remote Transmitter “Checklist for Level-ECEP” has been submitter to email: tco.level@se.com
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-29 12:16 PM
Thanks for the question/request!
ECEP request will have to go in to tco.level@se.com as the remote is not a standard offering anymore.
You may also consider IMV31 as an alternative or backup technology.
We've used those successfully on several boiler level applications before.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-29 12:16 PM
Thanks for the question/request!
ECEP request will have to go in to tco.level@se.com as the remote is not a standard offering anymore.
You may also consider IMV31 as an alternative or backup technology.
We've used those successfully on several boiler level applications before.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-04-30 01:52 AM
Customer is preferred to go with Level Displacer Transmitter because they have another steam drum also used displacer type.
And I heard about IMV31 going to discontinue product in Dec 2020.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-24 06:27 AM
As this is a public forum I can't comment on any product lifecycles, roadmaps, etc.
Please take a look at the IMV31 and/or work with the TCO team for an ECEP request.
The Exchange is *not* a substitute for our TAC (fielddevices-support@se.com) or TCO (tcoi.level@se.com) teams. They are our official technical experts.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.