Level Transmitter 244LD/144LD Steam Boiler Application
I have 3 Level Transmitters Model 144LD-22LKRSEA4PP2H-A on Steam Boiler (320°C and 120 Barg).
The Problem is the reading from the 3 Transmitters are different due to High Temperature influence on the Transmitter Sensor.
Although the Finger Print is loaded on the 3 Transmitters but there is a deviation in reading between the 3 Transmitters.
Also the Displacer Chamber is isolated from the High Temperature
I tried several times to zero the Transmitters at field (At High Temeprature) but the problem happened again after some time.
Also I changed the Transmitter with the equivalent 244LD Levelstar but the Problem also happened.
So what is the solution?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-22 06:25 AM
You may try fielddevices-support@schneider-electric.com email for support. Good luck!