PLC To PLC Communication (Siemens & Schneider )

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • PLC To PLC Communication (Siemens & Schneider )
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
MiretteMMikhaiil
Crewman MiretteMMikhaiil
Crewman

Posted: ‎2022-12-15 06:02 AM

1 Like
11
15258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-15 06:02 AM

PLC To PLC Communication (Siemens & Schneider )

Dear Community , 

 

I'm having a Simens PLC (Profinet communication ) and i would like to communicate with it M580 Schneider PLC , how to do it ? 

Is it possible by having a Prosoft gateway (Profinet to Modbus TC/IP ) or do you have another recommendation ? 

 

Thanks a lot for your support . 

Labels
  • Labels:
  • Smart Design & Engineering
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Svenmj
Ensign Svenmj Ensign
Ensign

Posted: ‎2022-12-15 06:36 AM . Last Modified: ‎2022-12-15 06:38 AM

2 Likes
0
15245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-15 06:36 AM . Last Modified: ‎2022-12-15 06:38 AM

If the Siemens PLC is in the 1200 or 1500 series you could use Modbus TCP communication. You can set M580 as Modbus Server and the Siemens PLC collect data as Modbus Client. As I remember you use the MB_Client block in the Communication Library in the TIA portal

 

You could also set it up the other way around Siemens as Modbus Server (Using MB_Server) Function Block and the use the IO Scanner in M580

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-12-16 02:55 AM

1 Like
0
15234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-16 02:55 AM

Modbus TCP is not longer a problem for the competitor PLC. You could find a documentation here .

The biggest pain point or in other words a point which could confuse are the definition of the register.

Siemens use for my opinion the strange definition were you add in front of the read out value the function code. As example MW10 must be define as 40010. And if you use 32Bit data types you have to rearrange the bytes. Because Siemens use a different Byte order to everybody else (Big/Little Endian Problem). 

 

And at least look for the Unit id. I´m not familar with the M580 maybe you need to use a different Unit ID then the default 255.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

shanwaaz
shanwaaz
Cadet

Posted: ‎2023-02-28 09:58 PM

0 Likes
0
15023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-28 09:58 PM

Yes, it is possible to communicate between a Siemens PLC with Profinet communication and a Schneider M580 PLC. One option is to use a ProSoft gateway that can convert Profinet protocol to Modbus TCP/IP.

Here are the steps to establish communication between the two PLCs:

  1. Connect the ProSoft gateway to the Siemens PLC using a Profinet cable.
  2. Connect the ProSoft gateway to the Schneider M580 PLC using an Ethernet cable.
  3. Configure the ProSoft gateway to map the data from the Siemens PLC to the appropriate Modbus TCP/IP addresses on the Schneider M580 PLC.
  4. Configure the communication settings on both PLCs to ensure they are compatible.

In addition to the ProSoft gateway, there are other devices and software that can facilitate communication between the two PLCs, such as Anybus gateways, HMS Industrial Networks gateway, and Schneider Electric's Unity Pro software. The choice of device or software will depend on the specific requirements of your application and the compatibility of the PLCs.

Reply

Link copied. Please paste this link to share this article on your social media post.

hardik
hardik
Cadet

Posted: ‎2023-04-26 09:52 PM

1 Like
0
14642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-26 09:52 PM

Yes, it is possible to communicate between a Siemens PLC with Profinet communication and a Schneider M580 PLC using a ProSoft gateway that converts Profinet to Modbus TCP/IP.

To establish communication between the two PLCs using the ProSoft gateway, follow these steps:

  1. Configure the ProSoft gateway: First, you need to configure the ProSoft gateway to convert the Profinet protocol used by the Siemens PLC to Modbus TCP/IP protocol used by the Schneider M580 PLC. This can typically be done using the ProSoft Configuration Builder software, where you can set the IP address of the Siemens PLC, the Modbus slave ID of the Schneider M580 PLC, and define the mapping of data between the two PLCs.

  2. Connect the ProSoft gateway: Connect the ProSoft gateway to both the Siemens PLC and the Schneider M580 PLC using Ethernet cables. Ensure that the IP addresses of the gateway, Siemens PLC, and Schneider M580 PLC are all on the same subnet.

  3. Write programs on both PLCs: Using the respective programming software for each PLC, write the necessary programs to read and write data between the two PLCs using the Modbus TCP/IP protocol. This will involve defining the addresses and types of data to be exchanged, as well as the communication settings such as the IP address and port number.

  4. Test communication: Once the programs are written, you can test communication between the two PLCs by exchanging data and verifying that the data is being correctly received and interpreted on both sides.

Alternatively, you could also consider using other communication protocols that are supported by both the Siemens PLC and Schneider M580 PLC, such as OPC UA or Ethernet/IP, and use a suitable communication module or gateway to establish communication between the two PLCs.

Reply

Link copied. Please paste this link to share this article on your social media post.

nathan_schiavo
nathan_schiavo
Cadet

Posted: ‎2023-04-27 08:17 AM

1 Like
0
14623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-27 08:17 AM

As others have mentioned, the 1200 and 1500 have a library for Modbus but so do S7-300 and 400 and comm modules like CP343. they can do both client and server while still talking profinet to other things on the same port. If you really like coding you can create a direct socket connection with TCON TSEND and TREC but that would be a bit of work and might as well use a library that has familiar functionality of Modbus already. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Fadzil
Fadzil
Cadet

Posted: ‎2025-03-05 06:00 PM

0 Likes
0
2130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 06:00 PM

Hi All, can Schneider M580 with modbus TCP be able to communicate Siemens VFD Drives with Profinet protocol?

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2025-03-05 09:37 PM

0 Likes
2
2097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-05 09:37 PM

The question is which VFD do you mean in detail?

Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-06 12:47 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-06 12:47 AM

... and if you connect both through OPCUA, OPCUA is native to both PLCs. Wouldn't this be simpler?

Reply

Link copied. Please paste this link to share this article on your social media post.

Fadzil
Fadzil
Cadet

Posted: ‎2025-03-13 09:06 PM

In response to Bastian_Schmitz
0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 09:06 PM

Sinamic S120 CU320-2 PN with Modicon M580. The Siemens VFD uses Profinet Protocol. How do we link these two devices to communicate? Previously, we used the Profibus protocol, and I am using PMEPXM0100 to communicate it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Fadzil
Fadzil
Cadet

Posted: ‎2025-03-14 01:08 AM

In response to Bastian_Schmitz
0 Likes
0
1725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 01:08 AM

Hi Bastian,

 

I must communicate the Sinamic S120 CU320-2 PN with Modicon M580—the VFD using profinet protocol. Need help to communicate these two devices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-24 01:37 AM

0 Likes
0
1488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 01:37 AM

Hello my friend @Fadzil 

Unfortunately, the M580 doesn't have the Profinet protocol.

 

BR

Ricard

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of