Hi,
I have HMIST6700 HMI. I need to show and control data from 4 different PLCs over modbus Ethernet. Is it possible using different symbol links in operator terminal expert. What is the maximum limit a single HMI6700 can communicate with different PLCs over modbus ethernet protocol?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-11 01:56 AM
Hi
Yes you can use diferent symbol-links in EOTE.
If the HMI act as Slave then the max. connection is 20 and if the HMI act as Master the max. connection is 64.
Greetings