Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84770members
354204posts

Modicon M172 Can-Bus Master with TM172E28R slave

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Solved
Mick0275
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
2
497

Modicon M172 Can-Bus Master with TM172E28R slave

Hello, 

 

I am using a expansion module TM172E28R on a TM172PDG42R controller with Machine Expert - HVAC software. 

I have setup my controller and software exactly like in this video from Schneider: https://www.youtube.com/watch?v=pyJA31G2yQk&list=PLa7UGrWOTyjlgMo0lD4eVCV0zFQYxbLoa&index=7 

I have setup up the controller as Can-Bus Master address 125 and the TM172E as slave address 1, also the dip switches are set (4-5-6 all off), the dip switcdh number one is on and is the EOL resistor. 

I have also added a 120 Ohm resistor on the Can-Bus terminal from the M172P. 

Somehow i cannot get the Master running with the slave running. 

The sys variables for the CANbus communication is all zero. 

I also have a input from the expansion module in my watch and its always false (voltmeter shows me 24VDC). 

Is there anything what I can try else? Or is there a setting i need to set that is not in the manual? 

The Firmware of TM172P is "596.10".

 

Any help is appreciated. Thank you.

 

Regards, 

 

Michael

Tags (2)

Accepted Solutions
Bastian_Schmitz
Commander Commander
Commander
0 Likes
1
488

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?

See Answer In Context

Tags (1)
2 Replies 2
Bastian_Schmitz
Commander Commander
Commander
0 Likes
1
489

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Did you made a download all? Only in that case the CONNEC.PAR which is used for the communication will be downloaded. On the expansion is near the CAN Port a LED. Is this LED flashing? What is the status of sysCANopenNodeStauts[3]?

Tags (1)
Mick0275
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
0
281

Re: Modicon M172 Can-Bus Master with TM172E28R slave

Thanks for your help, that LED was not flashing, it was a wire mistake on the bus. 

It works now.

Tags (1)