Which Port i Can use for Modbus TCP Communication for - P582020, with Other Modbus Devices, and How to Do that ?
As Following the Instruction Video, i couldn`t Find Model Family
https://www.youtube.com/watch?v=QhkIQCOyxjo
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-28 10:47 AM
Hi ,
I found the issue, Actually Slave ID, needs to be Written beside the Address, but this wasn`t mentioned either in the Help - Documents for ADDMX or the Videos.
After Adding Slave ID, it started Reading and Writing
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-25 03:13 AM
Hello,
M580 networking is configured using DTM configuration (open DTM Browser) not the Communication-Networks (this is for M340).
Refer to this video: https://www.youtube.com/watch?v=piDpLjMxmyw
You can use the IO-scanning as shown in the video, or use READ_VAR/WRITE_VAR:
https://www.youtube.com/watch?v=usLS7yuiF6s
IO-Scannin is Limited to Modbus functions 3&16 (read/write %MW or 4xxxxx references)
Read_VAR/WRITE_VAR support more Modbus functions (see manual or help in Unity/ECE)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-28 01:43 AM
Many Thanks Roozee.
I have used the READ_VAR & WRITE_VAR Blocks form M580, but i amn`t able to Read or Write to the slave, is there a Problem with my Setup ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-28 02:52 AM
Remove (temporarily) the WRITE_VAR, as it's not configured properly, and set the timeout value in CONTROL[2] to 10. Timeout of 0 will "hang" the function when something is wrong.
In that case you should see CONTROL[0] changing and CONTROL[1] should become 0.
I'm not familiar with the Modbus SLAVE program, but can you try to set the Modbus Slave ID to 255?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-28 10:47 AM
Hi ,
I found the issue, Actually Slave ID, needs to be Written beside the Address, but this wasn`t mentioned either in the Help - Documents for ADDMX or the Videos.
After Adding Slave ID, it started Reading and Writing