M580 redundant IPs

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • M580 redundant IPs
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
Modicon M580
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
the18
Crewman the18
Crewman

Posted: ‎2025-03-21 02:22 AM

0 Likes
6
558
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-21 02:22 AM

M580 redundant IPs

Hello, I have a system with two M580 redundant with this configuration:

the18_0-1742548293064.png

Rack: BMEXBP0400 / CPU: BMEH582040 / eNOC: BMENOC0301

and this is my network:

the18_1-1742548412576.png

Now I have a SCADA and two HMIs that needs to connect to the PLCs and so far I am connecting to them using the Primary eNOC @IP "192.168.3.95" but it seems that the Secondary doesn't swap to the mains @IP automatically when the main is off, is there something I am missing in my configuration or what ? because nor the SCADA nor the HMIs are getting any data when the primary is off.

Because I am used to working with Siemens 17-1500RH and the PLCs create a 3rd shared @IP that the main PLCs use.

SCADA is connected through Kepware server Modbus Suite and the HMI is the HMIST6600.

another question: Is the M580 secondary PLC picks up control on the spot or does it needs operator intervention and only preserves the Data; if so, where can I configure it.

Best regards.

Labels
  • Labels:
  • Connected Products
  • Cybersecurity
  • Training
  • Tags:
  • Control Expert
  • english
  • ip address
  • m580
  • M580 HSBY
  • M580 Redundant
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-25 03:50 AM

1 Like
0
457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 03:50 AM

Hello @the18 ,

 

This typically occurs because the PAC M580 doesn't have time to synchronize task data.

 

The MAST_SYNCHRONIZED, FAST_SYNCHRONIZED, and SAFE_SYNCHRONIZED variables indicate whether the database exchange between the Primary and Standby PACs was successful.


If not, the task cycle time must be increased:
MAST MAST task period %SW0 > Last cycle execution time (in ms) %SW30
FAST FAST task period %SW1 > Last cycle execution time (in ms) %SW33
SAFE SAFE task period %SW4 > Last cycle execution time (in ms) %SW42

 

 

Ricard_0-1742899504892.png

Configuring MAST/FAST Tasks
The duration of the Data Pack/Unpack process depends primarily on the number of DFB instances to be exchanged.
Data Pack/Unpack
Copies the values ​​of all variables into memory blocks, preparing for the data transfer.
All allocated variables in one memory block.
All unallocated variables in one memory block.
One DFB instance in one memory block.

Ricard_1-1742899570810.png

What happens when the Scan time is too short?

Ricard_2-1742899598607.png

Situations that may affect this:


A large number of DFBs to perform Pack/Unpack takes longer (1 ms per 100 DFBs).
A MAST task period that is too short.


Solutions:

  • Deselect DFBs to be swapped.
  • Recalculate every cycle.
  • Higher period.

 

I recommend that you review the following document, the Exchanging M580 Hot Standby Data section

https://download.schneider-electric.com/files?p_Doc_Ref=NHA58880&p_enDocType=User+guide&p_File_Name=...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-23 12:09 AM

1 Like
0
528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-23 12:09 AM

hello my friend @the18 

Yes, the secondary takes control, you can share the pictures again, they aren't displayed correctly.

Also share an image of the CPU and NOC network configuration, as well as the Control Expert connected to the CPU.

BR

Ricard

Reply

Link copied. Please paste this link to share this article on your social media post.

the18
Crewman the18
Crewman

Posted: ‎2025-03-24 03:19 AM

0 Likes
0
501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 03:19 AM

Hello @Ricard ,

Please find attached the requested images:

601.jpg : M580 Network configuration

602.jpg: NOC Network configuration

603.jpg: Ethernet network for all devices

604.jpg: Control expert version informations

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-24 03:46 AM

1 Like
0
492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 03:46 AM

It appears you're connecting correctly.
Have you performed swap tests? Can you display the PLC status in runtime?

Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
Lieutenant ciupol
Lieutenant

Posted: ‎2025-03-24 09:13 AM

1 Like
0
473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-24 09:13 AM

They should swap automatically and bumplessly. Make sure that your controllers are matched and the secondary is in RUN_STBY/EQUAL state. Also add operator screen to your project from Control Expert ISO from folder "\Extras\Operator Screens \m580 hsby operator screen v11.xcr" and provide screenshot of this screen.

Reply

Link copied. Please paste this link to share this article on your social media post.

the18
Crewman the18
Crewman

Posted: ‎2025-03-25 02:16 AM

0 Likes
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 02:16 AM

Hello @Ricard @ciupol ,

Thank you for your replies; I tried the swap and it seems to be working fine; I had a problem with NOSYNC because of a low MAST periode, I had "20ms" but i made it "35ms" and now it seems to be functionning well;

Many thanks to you guys and the best of regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-25 03:50 AM

1 Like
0
458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-25 03:50 AM

Hello @the18 ,

 

This typically occurs because the PAC M580 doesn't have time to synchronize task data.

 

The MAST_SYNCHRONIZED, FAST_SYNCHRONIZED, and SAFE_SYNCHRONIZED variables indicate whether the database exchange between the Primary and Standby PACs was successful.


If not, the task cycle time must be increased:
MAST MAST task period %SW0 > Last cycle execution time (in ms) %SW30
FAST FAST task period %SW1 > Last cycle execution time (in ms) %SW33
SAFE SAFE task period %SW4 > Last cycle execution time (in ms) %SW42

 

 

Ricard_0-1742899504892.png

Configuring MAST/FAST Tasks
The duration of the Data Pack/Unpack process depends primarily on the number of DFB instances to be exchanged.
Data Pack/Unpack
Copies the values ​​of all variables into memory blocks, preparing for the data transfer.
All allocated variables in one memory block.
All unallocated variables in one memory block.
One DFB instance in one memory block.

Ricard_1-1742899570810.png

What happens when the Scan time is too short?

Ricard_2-1742899598607.png

Situations that may affect this:


A large number of DFBs to perform Pack/Unpack takes longer (1 ms per 100 DFBs).
A MAST task period that is too short.


Solutions:

  • Deselect DFBs to be swapped.
  • Recalculate every cycle.
  • Higher period.

 

I recommend that you review the following document, the Exchanging M580 Hot Standby Data section

https://download.schneider-electric.com/files?p_Doc_Ref=NHA58880&p_enDocType=User+guide&p_File_Name=...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of