M580 HSBY High-Capacity Daisy Chain Loop (HCDL)

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • M580 HSBY High-Capacity Daisy Chain Loop (HCDL)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
31
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
Modicon M580

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
TheLegendTMX
Crewman TheLegendTMX
Crewman

Posted: ‎2025-01-20 05:58 AM

0 Likes
6
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-20 05:58 AM

M580 HSBY High-Capacity Daisy Chain Loop (HCDL)

Dears,

We have a redundant M580 HSBY system divided into two separate, distant, and identical locations that should serve as one system.

Each location contains:

  • One CPU
  • Two RIO drops
  • Two main network switches of the following type:
    "SGS-6310-48P6XR," Planet L3 48-Port 10/100/1000T 802.3at PoE + 6-Port 10G SFP+ Stackable Managed Switch

The available fiber link between the two locations is designated for:

  1. Linking the main network switches in a ring.
  2. Linking the two CPUs via the SFP HSBY connection.

Referring to the Modicon M580 Complex Topologies System Guide, Page 177, we need your recommendations for implementing the High-Capacity Daisy Chain Loop (HCDL) architecture in this M580 HSBY system.

We are considering establishing a dedicated VLAN on the main network switches to isolate HCDL traffic from other network traffic.

Question:
Is there anything specific to consider within the main switches or the M580 HSBY configuration for this setup?

Your advice and insights will be greatly appreciated.

Thank you in advance!

Labels
  • Labels:
  • Connected Products
  • Smart Design & Engineering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-01-21 02:47 AM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-21 02:47 AM

Hello TheLegendTMX,

 

It would be convenient if you shared in a schematic form the architecture that you propose, so that we can get an idea of ​​what you are proposing.
Just remember that the HSBY Link must be a dedicated point-to-point connection without elements between CPUs.

 

The architectures proposed in the document you mention are validated with Schneider Dual Ring equipment. If you want to use other Switch devices, I would recommend consulting your country's technical support as it requires a thorough analysis of the entire architecture.

I would advise you to review the following manual

 

Modicon M580 HotStandby System Planning Guide for Frequently Used Architectures

https://download.schneider-electric.com/files?p_Doc_Ref=NHA58880&p_enDocType=User+guide&p_File_Name=...

 

BR

Ricard

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

TheLegendTMX
Crewman TheLegendTMX
Crewman

Posted: ‎2025-01-28 11:28 PM

0 Likes
0
296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 11:28 PM

Dear Ricard,

Thank you for your prompt response and valuable insights.

I have attached the schematic of our current network architecture for your review and convenience. As mentioned earlier, we have ensured that the HSBY link is a dedicated point-to-point connection without any elements between the CPUs, as recommended.

 

Question:
Is there anything specific to consider within the main switches or the M580 HSBY configuration for this setup?

We appreciate your expertise and look forward to your advice.

Best regards,

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Ensign Hennie_Smith Ensign
Ensign

Posted: ‎2025-01-29 09:11 PM

0 Likes
0
282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-29 09:11 PM

Hi, No issue with your architecture in terms of the HSBY link on Single mode fiber. However the 

  • Two main network switches of the following type:
    "SGS-6310-48P6XR," Planet L3 48-Port 10/100/1000T 802.3at PoE + 6-Port 10G SFP+ Stackable Managed Switch

is a problem. Schneider only recommend the use of BMXNRP cards or the

Extended Modicon switches in the RIO network between the CPU and the CRA cards in the RIO's. Reason is there are a number of specific  configuration settings to be done to guarantee the response and recovery times. The PLC tag the RIO comms VLAN 1 which cannot be changed as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-01-29 11:14 PM

0 Likes
0
267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-29 11:14 PM

Hello All

 

Everything that the colleague says is correct. I advise you to review the following document and to propose the architecture to your Schneider Electric contact or the Technical Support of your country.

 

Modicon M580 Complex Topologies, System Guide

https://www.se.com/us/en/download/document/NHA58892/

 

Best Regards

Ricard 

Reply

Link copied. Please paste this link to share this article on your social media post.

TheLegendTMX
Crewman TheLegendTMX
Crewman

Posted: ‎2025-01-30 12:01 AM

0 Likes
1
247
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 12:01 AM

Dear Hennie,

Thank you for your valuable feedback.


We kindly request detailed information on the specific configuration settings required to ensure the appropriate response and recovery times for the RIO network. We believe these settings can be implemented on our existing Layer 3 network switches (SGS-6310-48P6XR).

Additionally, we would appreciate clarification on your statement:

"The PLC tag the RIO comms VLAN 1 which cannot be changed as well."

Could you please elaborate on the significance of this constraint and its potential impact on our architecture?

Looking forward to your advice.

Best regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Ensign Hennie_Smith Ensign
Ensign

Posted: ‎2025-01-30 02:36 AM . Last Modified: ‎2025-01-30 02:37 AM

In response to TheLegendTMX
0 Likes
0
246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-30 02:36 AM . Last Modified: ‎2025-01-30 02:37 AM

Hi,

The PLC CPU to RIO uses Vlan 1. The PLC tags all communication to the RIOs and there is no option to change this to a different Vlan.  Your drawing indicated you would like Vlan 2 for the RIO comms but that is not possible.

 

Regarding the SGS switches, your switch would most probably incorporate all the functions, however Schneider cannot guarantee the correct operation with any other switch than the Extended Modicon switches which has gone through thorough validation. As Ricard indicated, best to stick to the recommended architectures to ensure a solid solution or contact your local technical support to assist.

 

BR

Hennie

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of