Posted: 2025-03-19 06:01 PM
I'm using M262 plc with lxm32s servo and i want to release the brake but i cannot find any parameter changing method or function block in the new plc open mc library.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-21 04:49 AM
You can configure a digital input of the LXM32 for this function.
Configure the digital input as reHb, and activating it will release the brake.
| 40 / Release Holding Brake / rEhb: Releases the holdingbrake |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-22 10:37 AM
Thank you very much for the reply, but is there a way to release the brake from the software directly.