Communication between M340 and Cube20 I/O module with Ethernet/IP

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Communication between M340 and Cube20 I/O module with Ethernet/IP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
Kik
Crewman Kik
Crewman

Posted: ‎2025-03-10 04:22 AM

0 Likes
4
1326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 04:22 AM

Communication between M340 and Cube20 I/O module with Ethernet/IP

Hello all,

 

I'm a french student working on a project. I bought a M340 PLC with at least a NOC0401 on it.

The PLC is working, I've set a IP@ on it.

I also have a Cube20 BN-E/IP DI8 module, working with Ethernet/IP protocol.

Both have IP@ on the same network. From my laptop, I can ping both.

 

Now I'm trying to read inputs from my Cube20 on my PLC.

I added it in the "DTM Browser" as Generic EDS Device DTM and configured IP@. I'm able, from the DTM Browser on Control Expert to "Connect" to the Cube20 (right clic on it and CONNECT).

 

I don't know what to do from now. Any suggestion ?

 

In advance, thanks

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ciupol
Lt. Commander ciupol
Lt. Commander

Posted: ‎2025-03-10 12:32 PM

2 Likes
1
1298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 12:32 PM

Do get the implicit data exchange going you have to configure IO instances and data sizes. Double click your generic DTM in DTM browser and you should see screen similar to the attached screenshot. You need to configure what I highlighted in yellow. You get that information from device manual. I am looking at file 56005_hdb_e_16.pdf downloaded from Murr Electronic website. On page 25 it gives you instance numbers and starting on page 22 it tells you how to obtain data size. Once you set it up you should be good to go and you see data in your device DDT.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
ciupol
Lt. Commander ciupol
Lt. Commander

Posted: ‎2025-03-10 12:32 PM

2 Likes
1
1299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-10 12:32 PM

Do get the implicit data exchange going you have to configure IO instances and data sizes. Double click your generic DTM in DTM browser and you should see screen similar to the attached screenshot. You need to configure what I highlighted in yellow. You get that information from device manual. I am looking at file 56005_hdb_e_16.pdf downloaded from Murr Electronic website. On page 25 it gives you instance numbers and starting on page 22 it tells you how to obtain data size. Once you set it up you should be good to go and you see data in your device DDT.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Kik
Crewman Kik
Crewman

Posted: ‎2025-03-12 02:20 PM

In response to ciupol
0 Likes
0
1266
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 02:20 PM

Hi Ciupol. Thank you so much for your help, I managed to read the inputs with your help and the doc.

Now I'm wondering how to use this information, because I see that the same variable ("Cube20_IN.Free0[0]") changes depending on which input is activated as you can see on my screenshots.

If I activate input 1, value is 1. Input 2, value 2. Input 3, value 4. Input 4, value 8 and so one...

Do you know if this is the expected behavior?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
Lt. Commander ciupol
Lt. Commander

Posted: ‎2025-03-19 05:46 AM

1 Like
1
1151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 05:46 AM

Kik, yes it absolutely makes sense. Bit 0 of Cube20_IN.Free0[0] Byte is status of input 1, bit 1 of Cube20_IN.Free0[0] Byte is status of input 2 etc. In your animation table display numbers as binary (right click on variable number and select Display format -> Binary) and it will be obvious for you what is going on. Again you have to use manual for your module. Look specifically in sections 4.5 and 6.1 of manual mentioned in my previous post.

Reply

Link copied. Please paste this link to share this article on your social media post.

Kik
Crewman Kik
Crewman

Posted: ‎2025-03-21 01:09 PM

In response to ciupol
0 Likes
0
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-21 01:09 PM

Thank you very much once again

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore