M262 plc with lexium 32s brake release
I'm using M262 plc with lxm32s servo and i want to release the brake but i cannot find any parameter changing method or function block in the new plc open mc library.
- Labels:
-
Process Automation Talks
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-21 04:49 AM
You can configure a digital input of the LXM32 for this function.
Configure the digital input as reHb, and activating it will release the brake.
40 / Release Holding Brake / rEhb: Releases the holdingbrake |
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-22 10:37 AM
Thank you very much for the reply, but is there a way to release the brake from the software directly.