I am looking for the following data about temperature transmitter RMTK90BD:
1)At temp 150 C (302F) the voltage at the type K thermocouple is 6,138 mv
2)At temp 250 C (482F) the voltage at the type K thermocouple is 10,153 mv
What is the output of the RMTK90BD in 0-10 V or 4-20 ma ?
Where is that info ? I did not find anything relevant at the documents .
Manos
  • Smart Design & Engineering
Bastian_Schmitz
Admiral
Posted: ‎2021-01-19 11:10 AM
The 0-10V output should be linear to the Temperature Signal.
In your case 150°C should generate 1,25V and 250°C should generate 2,083V.
You can find further informations about wiring in the follow catalog
Link to Zelio transmitter catalog
Bastian_Schmitz