Info about temperature transmitter RMTK90BD:
Hello
I am looking for the following data about temperature transmitter RMTK90BD:
1)At temp 150 C (302F) the voltage at the type K thermocouple is 6,138 mv
2)At temp 250 C (482F) the voltage at the type K thermocouple is 10,153 mv
What is the output of the RMTK90BD in 0-10 V or 4-20 ma ?
Where is that info ? I did not find anything relevant at the documents .
Thanks
Manos
- Labels:
-
Smart Design & Engineering
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-19 11:10 AM
The 0-10V output should be linear to the Temperature Signal.
In your case 150°C should generate 1,25V and 250°C should generate 2,083V.
You can find further informations about wiring in the follow catalog
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-19 11:10 AM
The 0-10V output should be linear to the Temperature Signal.
In your case 150°C should generate 1,25V and 250°C should generate 2,083V.
You can find further informations about wiring in the follow catalog