Hello
I want to create a small control unit for an electric oven at the range 50-300 C (122-572 F).
Are there the necessary parts (smart relay, signal conditioner, etc ) at the Zelio compact series ?
Or I must use the modular relays of Zelio series ?
Thanks Manos
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-13 10:50 PM . Last Modified: 2021-01-13 10:50 PM
Hello,
You can use Zelio Logic Compact or Modular.
It depend how you want to reach your goal.
With both approches you need an additional Temperatur Input.
In the Compact and DC voltage version you have 0-10V Analog Inputs.
These could be combined with zelio converters for thermocouples or PT100 Sensors to 0..10V (as an example RMTJ60BD ).
With the modular offer you have the possibility to add an Analog Input modul (SR3XT43BD ) which support PT100.
You can find on the product page also a configurator to choose the right PLC
Alternativ a solution based on TM221 could also be interresting. For these controller is a small temp probe cartidge modul available TMC2TI2 which supports also PT1000 and Thermocouple
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-13 10:50 PM . Last Modified: 2021-01-13 10:50 PM
Hello,
You can use Zelio Logic Compact or Modular.
It depend how you want to reach your goal.
With both approches you need an additional Temperatur Input.
In the Compact and DC voltage version you have 0-10V Analog Inputs.
These could be combined with zelio converters for thermocouples or PT100 Sensors to 0..10V (as an example RMTJ60BD ).
With the modular offer you have the possibility to add an Analog Input modul (SR3XT43BD ) which support PT100.
You can find on the product page also a configurator to choose the right PLC
Alternativ a solution based on TM221 could also be interresting. For these controller is a small temp probe cartidge modul available TMC2TI2 which supports also PT1000 and Thermocouple
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-17 04:33 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-01-17 04:33 PM
Hello Bastian
Thank you so much for your prompt response. It is very helpful.
I will start the project from the "end": The thermocouple side.
The RMTK80BD fulfill the requirements. I hope that finally I will find instructions of use .
Manos