Posted: 2022-12-09 03:23 AM
Can we display forced bits from Ecostructure control expert to citect studio scada?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-09 06:49 AM
This will depend on the controller that you are using and the communication method that you are using with Citect. The Analog Device DDT's in the Modicon M580 have a FORCED Status. If you are using the Schneider Electric OPC DA or UA server, you can gain access to this information directly.
This is a screen capture from the Analog Input Module.
This is a screen capture form the Analog Output Module.
For the Digital Input and Output you will need to use the IS_BIT_FORCED EF to detect the force status.
In addition, System Words %SW108 and %SW109 will provide a count of the number of forced digital and analog channels in the application.