ION9200 not showing total KW,KVA,KVAR on display

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • ION9200 not showing total KW,KVA,KVAR on display
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
13
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
Chiragshah
Crewman Chiragshah Crewman
Crewman

Posted: ‎2023-06-29 08:52 AM

0 Likes
4
2613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-29 08:52 AM

ION9200 not showing total KW,KVA,KVAR on display

Dear Team,

We have a problem in ION9200. Which is not showing Total KW,KVA,KVAR values on display. Meter is showing  all readings in Ion software and in modscan.

  1. Connect meter with ion enterprise and checked all basic settings- found ok.
  2. Inverse the current direction through ion setup to correct KW polarity.
  3. Upgrade the firmware to 4.0
  4. PQ meter Model: METSEIN92030
  5. PQ Meter serial number: MZ-2301A659-01

Meter is showing  all readings in Ion software and in modscan . screen shot attached. Meter is showing individual phase KW,KVA, KVAr readings but not showing total KW, KVA, KVar on its display. Video attached.

please help on the topic.

 

@Ramasamy_N 

Attachments
Labels
  • Labels:
  • ION9000
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2023-07-04 01:55 PM

0 Likes
1
2515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-04 01:55 PM

I believe you are mistaken about all readings showing correctly in Modscan (Modbus)
The phase A power reads as expected: -1.30e7 Watts (-13.0 MW), but total power reads -23.5 Watts (-0.000023 MW)
I suspect you've made a logic or scaling change somewhere in the framework between the Power Meter module (read by ION Setup's realtime screen) and the Data Mapping Module (used by Modbus, Display, and Web pages)
Please attach the framework that is on the meter (DCF or FWN file) using ION Setup's "Save to PC" or Select All and save to file with Designer

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2023-07-05 11:29 AM

0 Likes
0
2500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-05 11:29 AM

ION Setup real-time screen is presently designed to show Uncompensated power readings so if Transformer Losses is enabled, this would explain the difference between ION Setup and what is being read via Modbus/Front panel display.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 4
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2023-06-29 09:15 AM

0 Likes
0
2610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-29 09:15 AM

Hello @Chiragshah ,

 

Hard to say exactly what is happening from the images and screenshots alone. In ION Setup it is possible to view advanced mode (hold Ctrl and click on meter in left panel, same process to reverse). In Advanced mode, navigate to the Data mapping Measurement Module. Here you can see what is linked to the inputs, as well as read a snapshot of real time data. Find the kW, kVAR, kVA total inputs and confirm what you see on display matches what you see in ION Setup. If you righ click on the input you have the option to go to the register where this is coming from.

 

Using the above method you might be able to trace back through template to determine what is happening.

Otherwise recommend contacting your local technical support to start a case.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DanL
Captain DanL Captain
Captain

Posted: ‎2023-07-04 01:55 PM

0 Likes
1
2516
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-04 01:55 PM

I believe you are mistaken about all readings showing correctly in Modscan (Modbus)
The phase A power reads as expected: -1.30e7 Watts (-13.0 MW), but total power reads -23.5 Watts (-0.000023 MW)
I suspect you've made a logic or scaling change somewhere in the framework between the Power Meter module (read by ION Setup's realtime screen) and the Data Mapping Module (used by Modbus, Display, and Web pages)
Please attach the framework that is on the meter (DCF or FWN file) using ION Setup's "Save to PC" or Select All and save to file with Designer

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Robert_Lee
Admiral Robert_Lee Admiral
Admiral

Posted: ‎2023-07-05 11:29 AM

0 Likes
0
2501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-05 11:29 AM

ION Setup real-time screen is presently designed to show Uncompensated power readings so if Transformer Losses is enabled, this would explain the difference between ION Setup and what is being read via Modbus/Front panel display.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DanL
Captain DanL Captain
Captain

Posted: ‎2023-08-11 02:05 PM

In response to DanL
0 Likes
0
2270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-11 02:05 PM

It appears you have "Scale Revenue Parameters" set to OFF in your meter configuration. Please use ION Setup to update the configuration as shown below

DanL_0-1691787866249.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of