How to write address in ADDM function block

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • How to write address in ADDM function block
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Kik
Crewman Kik
Crewman

Posted: ‎2025-03-26 07:32 AM

0 Likes
10
464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-26 07:32 AM

How to write address in ADDM function block

Hello everyone,

 

I'm trying to use some functions like READ_VAR or DATA_EXCH to communicate with modbus devices on my M340.

Before that, I have to use ADDM function and to write the address.

 

This my configuration:

 

Screenshot 2025-03-26 152214.png

I'm using the NOC card on port #2. I assume that my address will be:

Kik_0-1742999050558.png

192.168.180.6 is my modbus device that I want to target.

 

I tried :

  • '0.2.2{192.168.180.6}0'
  • '0.2.2{192.168.180.6}1'
  • '0.2.1{192.168.180.6}'
  • '0.2.2{192.168.180.6}'

But I think it doesn't work because I have no request (capturing with Wireshark).

 

Do you have any idea ?

 

Thanks

 

 

Labels
  • Labels:
  • Smart Operations
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2025-03-27 12:40 AM

0 Likes
0
434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-27 12:40 AM

Hello my friend @Kik ,

 

There was a problem uploading the images, can you upload them again?

 

BR

Ricard

Reply

Link copied. Please paste this link to share this article on your social media post.

Fidencio
Fidencio
Cadet

Posted: ‎2025-03-28 12:26 AM

0 Likes
1
410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-28 12:26 AM

The correct syntax for the address string is crucial for successful communication. The general format for the address string in ADDM is 'r.m.c{IP_Address}e', where r represents the rack number (typically 0 for the main rack), m is the module number (the slot where the NOC module is installed), c refers to the channel number (the Ethernet port on the communication module), IP_Address is the target Modbus device’s IP, and e is the equipment number, which is the Modbus Unit ID.

 

For example, if your NOC module is in slot 2 and you're using port 2, targeting a device at 192.168.180.6 with a Unit ID of 1, the correct address string would be '0.2.2{192.168.180.6}1'. If your Modbus device uses a Unit ID of 0, then the string should be '0.2.2{192.168.180.6}0'.

 

If you’re not seeing any communication requests in Wireshark, there are a few things to check. First, ensure that the IP settings of both the PLC and the Modbus device are correctly configured and within the same subnet. Also, verify that the NOC module is properly set up to communicate over the selected port. Additionally, make sure your Modbus device is powered on and ready to accept connections.

 

If the communication still doesn’t work, confirm the correct Unit ID of your Modbus device, as some devices might require a different number instead of 1 or 0. To further troubleshoot, try using tools like ModScan or Modbus Poll from a PC to check if the Modbus device is responding and whether the network path is clear.

Reply

Link copied. Please paste this link to share this article on your social media post.

JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
Lieutenant JG

Posted: ‎2025-03-28 09:02 AM

In response to Fidencio
0 Likes
0
399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-28 09:02 AM

The channel designation in the r.m.c isn't the port number, it's the logical channel in the module.  In an M580 controller, for example, Ethernet messaging uses channel 3.  There is only one channel in the NOC, channel 0.  So the correct usage with an ADDM is '0.2.0{ip address}unit ID if used'.  For an ADDMX it would be '0.2.0.{ip address}unit ID if used'.  The period behind the r.m.c is an easily missed small difference.

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2025-03-30 10:19 AM . Last Modified: ‎2025-03-30 10:19 AM

0 Likes
0
357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-30 10:19 AM . Last Modified: ‎2025-03-30 10:19 AM

I shared my m340 program screen. it has been working since 2018. Could you please look over at attached.si2.jpgsi1.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
Lieutenant JG

Posted: ‎2025-03-31 08:02 AM

0 Likes
1
333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-31 08:02 AM

Hello Ismail,  Your logic looks fine.  Did you have a question on it?  The difference between what I see in the screen shot and the original question is the use of the Ethernet port configuration name instead of the r.m.c notation.  In M340, because we define a network, name it, and attach it to a module, we can use the name.  In either M580 or M340, the r.m.c notation works.

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2025-03-31 11:47 PM

In response to JerryBartlemay
0 Likes
0
318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-31 11:47 PM

No, I did not have a question. I answered based on the question title so that the answer would remain under the same title in case similar questions arise in the future.

Reply

Link copied. Please paste this link to share this article on your social media post.

Rico94
Crewman Rico94 Crewman
Crewman

Posted: ‎2025-04-02 04:03 AM

0 Likes
0
290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-02 04:03 AM

Hello all, can you define when use an ADDM instead ADDMX?thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

MetinSakin
Ensign MetinSakin Ensign
Ensign

Posted: ‎2025-04-03 12:05 AM

1 Like
2
271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-03 12:05 AM

ADDM is for M340 

ADDMX is for M580 

Metin Sakin
Reply

Link copied. Please paste this link to share this article on your social media post.

Rico94
Crewman Rico94 Crewman
Crewman

Posted: ‎2025-04-03 12:31 AM

In response to MetinSakin
0 Likes
1
267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-03 12:31 AM

Thanks for the response.

But i'm surprise because actually i'm using ADDM with M580 and it works fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
Lieutenant JG

Posted: ‎2025-04-04 07:25 AM

In response to Rico94
0 Likes
0
226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-04 07:25 AM

ADDM works for both M580 and M340 in the local racks or for Ethernet devices on ERIO.  ADDMX also supports messaging through an ERIO drop to NOM modules.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of