Hi
I need help regarding the connection between IFM and PLC's.
I have Masterpact MTZ1-10 H1 and i have it successfully connected to lv434000 modbus.
I now need wiring diagrams or something to connect it to a unitronics plc.
So the modbus uses rj45 and i think it outputs it's thing trough rs485.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-20 10:21 PM
Hi MikyE,
You could find the Pin wiring of the RJ45 plug in the instruction sheet.
You need normaly at every SE Product for RS485 Modbus Pin 4 and Pin 5
If you use a standard patch cable you have to use the blue and the blue with wire.
For easier wiring you could use
or
I did not know which kind of plug you need on the Unitroncs HMI/PLC.
You could find additional adapter cables in the SE Harmony HMI offer.
Catalog HMIST6 (adapter cable page 22..24)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-01 12:04 AM
@Bastian_Schmitz wrote:Hi MikyE,
You could find the Pin wiring of the RJ45 plug in the instruction sheet.
You need normaly at every SE Product for RS485 Modbus Pin 4 and Pin 5
If you use a standard patch cable you have to use the blue and the blue with wire.
For easier wiring you could use
or
RJ45 Open Style cable slope game
I did not know which kind of plug you need on the Unitroncs HMI/PLC.
You could find additional adapter cables in the SE Harmony HMI offer.
Catalog HMIST6 (adapter cable page 22..24)
Thank you, this question was also relevant to me.