Posted: 2021-08-29 05:38 PM
Hello all
So I have a HMISTU655 connected to a m221 plc.
I'm trying to display on the hmi a count every pulse sent from a coin acceptor connected to a plc input.
Every pulse is "worth" 50 cents and i need the HMI to display that count in euros.
I have set a counter on the m221, however the vijeo designer software doen't accepted as a variable and I'm unable to display that.
Also need a reset button on the hmi.
Any help would be greatly appreciated, as this is the last step of this project.
Thank you in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-23 06:46 AM
If you move the Count Value into a %MW area, you can read it in HMI
Same way resetting the Counter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-09-23 06:46 AM
If you move the Count Value into a %MW area, you can read it in HMI
Same way resetting the Counter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.