HMISTU655 Counting pulses

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Solved
JPalas
Crewman
Crewman
0 Likes
3
699

HMISTU655 Counting pulses

Hello all

 

So I have a HMISTU655 connected to a m221 plc.

 

I'm trying to display on the hmi a count every pulse sent from a coin acceptor connected to a plc input.

 

Every pulse is "worth" 50 cents and i need the HMI to display that count in euros.

 

I have set a counter on the m221, however the vijeo designer software doen't accepted as a variable and I'm unable to display that. 

 

Also need a reset button on the hmi.

 

Any help would be greatly appreciated, as this is the last step of this project.

 

Thank you in advance

 

 

Tags (1)

Accepted Solutions
Svenmj
Ensign Ensign
Ensign

Re: HMISTU655 Counting pulses

 

If you move the Count Value into a %MW area, you can read it in HMI

Same way resetting the Counter

 

CoinCount.png

See Answer In Context

Tags (1)
3 Replies 3
Rodrigo_Garcia
Administrator Administrator
Administrator
0 Likes
0
629

Re: HMISTU655 Counting pulses

Hello @TomDroll , would you know who can support on this? Thanks!

Rodrigo G. 


Industrial Automation Community manager

Tags (1)
Svenmj
Ensign Ensign
Ensign

Re: HMISTU655 Counting pulses

 

If you move the Count Value into a %MW area, you can read it in HMI

Same way resetting the Counter

 

CoinCount.png

Tags (1)
JPalas
Crewman
Crewman
0 Likes
0
598

Re: HMISTU655 Counting pulses

That was it. Works great.

Thank you so much

Tags (1)