FDR Assigning Mystery IP Address

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • FDR Assigning Mystery IP Address
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-24 02:08 PM

0 Likes
11
3432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 02:08 PM

FDR Assigning Mystery IP Address

Hello! I'm setting up FDR on a group of ATV340s. I'm running into an issue where two out of about 30 VFDs are getting assigned IP addresses that are not listed anywhere in my program/the FDR server list. For example:

 

I turn on DHCP for VFD named "ATV340VFD16" and am expecting the IP to be set to ***.***.4.16 but instead, once I've restarted the VFD, the IP is set to ***.***.249.248

 

I've checked and verified there's no duplicate device name on another VFD, there's no duplicate IP, and the name on the device matches exactly with the FDR server list. Has anyone experienced this before/have any idea why this is happening?

Labels
  • Labels:
  • Connected Products
  • Smart Design & Engineering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-24 02:33 PM . Last Modified: ‎2023-01-24 02:34 PM

0 Likes
4
3415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 02:33 PM . Last Modified: ‎2023-01-24 02:34 PM

Have you updated the FDR Server in the CPU, NOE or NOC that is communicating to the drive? This has to be done after every change.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-25 06:10 AM

In response to Robert_Willis
0 Likes
3
3397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:10 AM

The FDR server in the CPU shows the listing for that VFDs as named and addressed correctly. To be safe, I completely deleted the VFD from the program reinput them from scratch, readding them to the FDR server. This did not resolve the issue unfortunately.

 

What I find most confusing is that the IP addresses that are being assigned to these two VFDs aren't even close to address being used in the program/on the FDR server. I'm not sure where they are coming from.

Reply

Link copied. Please paste this link to share this article on your social media post.

Richard
Lt. Commander Richard Lt. Commander
Lt. Commander

Posted: ‎2023-01-25 06:22 AM . Last Modified: ‎2023-01-25 06:23 AM

In response to JSIA22
0 Likes
2
3395
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:22 AM . Last Modified: ‎2023-01-25 06:23 AM

Without the network architecture it is difficult to tell but have you checked the wider network for another DHCP server?

Reply

Link copied. Please paste this link to share this article on your social media post.

JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-25 06:33 AM

In response to Richard
0 Likes
1
3389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:33 AM

The system is currently pretty isolated right now. The VFDs are connected to an unmanaged switch which runs to a NOC. The NOC connects to the CPU. From there, there's currently no communication with a wider network.

Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-25 06:39 AM

In response to JSIA22
0 Likes
0
3386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:39 AM

Is the backplane port of the BMENOC module turned on? Based on your description it is possible that the FDR Server in the CPU and the NOC are both active. Have you ever attempted to connect the drive to the CPU? Please provide some details on "The NOC Connects to the CPU". Are you indicating that it is connected via the backplane or through a cable connection between the NOC and CPU.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-25 06:48 AM

0 Likes
2
3380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:48 AM

Sorry, my network description was not quite accurate! The VFD is connected to the unmanaged switch. The switch connects to the NOC which communicates with a CRA via the backplane. It's the CRA that communicates with the CPU through a cable connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-25 06:54 AM

In response to JSIA22
0 Likes
1
3378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 06:54 AM

Now you have me thoroughly confused on how your system is connected. Can you provide a detailed drawing?

Reply

Link copied. Please paste this link to share this article on your social media post.

JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-25 07:15 AM

In response to Robert_Willis
0 Likes
0
3367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 07:15 AM

I'm probably not explaining it correctly. I'm new to Scheinder tech and have only been on this particular project a few days, so I'm still figuring it out myself. I'm not authorized to post the drawing unfortunately, but I'll do my best to clarify!

 

The VFDs are all run to a remote I/O panel with a remote rack. There are multiple remote I/O panels, so the CRA modules between these remote I/O racks are connected in a ring network with the CPU in the main panel.

 

A VFD is connected to an unmanaged switch. The switch is connected to a BMENOS (I think I previously said NOC. Sorry!) module on the remote I/O rack. Through the backplane, the NOS communicates to a BMECRA module which is connected to the other remote I/O rack CRA modules and the main CPU in a ring network configuration.

 

I hope this makes more sense than my previous description. Appreciate all the help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Lieutenant JG Robert_Willis Lieutenant JG
Lieutenant JG

Posted: ‎2023-01-25 07:38 AM

0 Likes
2
3361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 07:38 AM

Based on your new description it appears that the M580 CPU is handling the communication to the various VFD's that are connected through a BMENOS0300 module that is located in the X80 remote I/O drop. Does the ATV340 have a local display connected to it? Have you updated the FDR server in the Modicon M580?

Reply

Link copied. Please paste this link to share this article on your social media post.

JSIA22
Crewman JSIA22
Crewman

Posted: ‎2023-01-25 07:50 AM

In response to Robert_Willis
0 Likes
1
3356
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 07:50 AM

Yes, that's the correct layout! The ATV340 does have a local display (ATV340U22N4E). The FDR server in the M580 has been updated. The identifier type is device name, which exactly matches with what is on the ATV340.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teaan
Lieutenant Teaan
Lieutenant

Posted: ‎2023-01-25 10:59 PM

In response to JSIA22
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 10:59 PM

I would suggest you setup the NOC card's service port as a mirroring port. Then use WireShark to see who answers the ATV340's DHCP request. This will give you place to start. If you don't see any requests coming through on the NOC that seems relevant do the same on the M580's service port. Finally if you don't see anything there, then if you have a managed switch available install it in place of the unmanaged switch and do the same test as close as possible to the drive. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore