ATS22C11Q and line contactor 3-wire control

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • ATS22C11Q and line contactor 3-wire control
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
31
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
KanG
KanG
Cadet

Posted: ‎2023-01-13 02:24 AM

0 Likes
4
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-13 02:24 AM

ATS22C11Q and line contactor 3-wire control

I have a softstarter ATS22C11Q and I want to control it with a three-wire circuit - with start and stop buttons .

From the point of view of reliability, I want to connect it according to the scheme indicated by the manufacturer (on the picture ).  There are 4 buttons on the diagram.

In what sequence are they pressed when starting and when stopping (how does this scheme work)?

How to make contactor KM1 turn off when we press stop.

What must be the power of transformer T1  (400/230V) ?

Attachments
Labels
  • Labels:
  • Smart Design & Engineering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-01-13 05:04 AM . Last Modified: ‎2023-01-13 05:04 AM

0 Likes
2
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-13 05:04 AM . Last Modified: ‎2023-01-13 05:04 AM

Your electrical drawing is correct, in order to initiate the sequence, S2 must be pressed on, it will allow KM1 to supply the starter, then S3 will initiate the motor starting with settings you entered in the Soft Starter (I mean ramp and current limitation). Stopping the motor can be done using S4, in this case it will follow deceleration as programmed in the soft Starter, but it can also be pressing S1, in this case the KM1 will open then motor will stop on freewheel. The power transformer has to be in accordance with all your sequnce components (KM1 coil plus CL1/2 consumption, advise to 100VA, add eventually fan if necessary depending on your duty cycle (see manual for this last topic).

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

KanG
KanG
Cadet

Posted: ‎2023-01-24 08:05 AM

In response to BJacqz
0 Likes
1
925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 08:05 AM

Thanks for your reply! To simplify the control, I decided to use the scheme with 2-wire control . I will use only two buttons - S1 and S2, with which I will control the linear contactor KM1 and with its normally open contact I will control the softstarter (instead of S3; to Li2). I hope the delay of the softstarter start command compared to pressing the S2 button is enough to avoid an alarm message. Li2 -> "run" , R2->"trip"  value. What is the difference in setting "trip" and "alarm" of relay R2 (or R1) - how much do the activation cases in the two modes overlap?  There are no detailed descriptions of the relay settings in the softstarter manual. Thank You!

Reply

Link copied. Please paste this link to share this article on your social media post.

KanG
KanG
Cadet

Posted: ‎2023-01-24 08:16 AM . Last Modified: ‎2023-01-24 08:32 AM

In response to KanG
0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 08:16 AM . Last Modified: ‎2023-01-24 08:32 AM

P.S. Freewheel stop (deceleration is off and not used).

Reply

Link copied. Please paste this link to share this article on your social media post.

BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-01-25 02:12 AM

0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-25 02:12 AM

The difference between trip and alarm is an alarm will only indicate there is a potential stop of the device, a trip will stop the device. As indicated, in the user's manual, "the alarm will indicate the presence of a non critical event" (example of thermal pre alarm coming before the thermal trip detection occurs). Hope this helps you...

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of