I hope this is the right spot for this question. I think I'm on the right track but can't seem to get this to work.
I have an elementary variable ARRAY [0..5] OF INT with some numbers and want to extract values from it with function blocks.
Attached is what I have so far. It does what I want but can't seem to get values I want past the 0/n location.
Thanks, Jeff Perau
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-15 09:27 PM
The EXTRACT block copies by bytes. You are using INTs which are 2 bytes long. SRC_POS needs to increment by 2 and CPY_NELEM should be 2 in order to get both bytes.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-15 09:27 PM
The EXTRACT block copies by bytes. You are using INTs which are 2 bytes long. SRC_POS needs to increment by 2 and CPY_NELEM should be 2 in order to get both bytes.