Establish TCP/IP Slave & Channel configuration is possible in PLC TM251MESE Ethernet Port-1

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Establish TCP/IP Slave & Channel configuration is possible in PLC TM251MESE Ethernet Port-1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-08-11 01:19 AM

0 Likes
3
2192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-11 01:19 AM

Establish TCP/IP Slave & Channel configuration is possible in PLC TM251MESE Ethernet Port-1

We have TH110 temp monitor 80 devices & this is communicating with ACTI9 A9XMWD100 ‘2’ device. (40 TH110 with 1st Acti9 & 40TH110 with 2nd Acti9)

 

Next, ACTI9 A9XMWD100 ‘2’ devices are connected to TM251MESE PLC Ethernet PORT-1.

 

Here the question is M251MESE Ethernet Port -1 (having default 2 ports) will support for Generic Modbus slave to configure Modbus TCP Slave & Channel configuration.

 

Attached hand marked System architecture for reference.

 

Motto: Get the TH110 devices temperature values in M251 PLC & same to be transfer through Modbus RTU (RS 485) communication to Scada PLC.

 

@BillP @Benji @Charles_Murison @Tom_Stevenson 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-08-12 07:54 AM

0 Likes
2
2176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-12 07:54 AM

Hello,

Yes this should be possible, but I´m not sure if Ethernet 1 could also act as Modbus Client.

So far I understand Ethernet 2 is for the field devices and Ehternet 1 is for laptop or SCADA.

You could use a TM4ES4 as switch.

 

But you need to map all needed values Manual from the Modbus Client Site (Modbus TCP) to the Mobdus Server Site (Modbus RTU) which goes to the SCADA PLC.

 

Please check if it is no problem that the RS485 on the TM251 is not isolated in you application.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-16 05:52 AM

In response to Bastian_Schmitz
0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-16 05:52 AM

Yes we need additional ethernet switch else we can not comply our requirement. 

 

Ethernet-1 (2 ports) will not support for TCP Slave devices But the port itself act as a Slave.

 

Many Thanks,

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-09-12 01:25 AM

In response to Bastian_Schmitz
0 Likes
0
2048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-09-12 01:25 AM

Hi,

 

we are unable to communicate 2 power Tag device which is having Modbus TCP/IP communication with using M251 PLC, used un managed Ethernet switch as per the suggestion, below is the sample SA.

 

Attached PLC program for your reference & necessary solution.

 

@Bastian_Schmitz 

Establish TCP/IP Slave & Channel configuration is possible in PLC TM251MESE Ethernet Port-1 

@Anonymous user 

Attachments
Working M251 PLC.zip
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore