Posted: 2023-02-21 06:29 AM
Hello,
I'm having an issue in Control Expert V15.2 where when I open up the DTM browser and attempt to connect to any ATV340 listed in the DTM browser I get a message saying: "Impossible to go in on-line mode" and then fails to connect. The ATVs have all been configured, I can ping them, run them from the program, and also connect to them via SoMove. Has anyone else encountered this issue before? I'm wondering if there's a setting in Control Expert I'm missing or some adjustment I need to make before I can connect to the drives in Control Expert?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-21 07:10 AM
My apologies. I'm newer to Control Expert (coming from Studio 5000). I'm not sure what you're referencing by master dtm?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-21 09:48 PM
@JSIA22 Please see the attached image below. Please make sure the IP, Gateway & Subnet mask set in the tool is the same as the device.
To launch this view in Control Expert double click on BMEP58_ECPU_EXT ( Master DTM ) and go to device list and set IP address, Subnet mask , Gateway and DHCP.
Once Set you should be able to connect
Link copied. Please paste this link to share this article on your social media post.