Citect V6.0 Connection with S7 300 CPU

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Citect V6.0 Connection with S7 300 CPU
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Citect SCADA

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
Mentor
Ensign Mentor
Ensign

Posted: ‎2024-07-11 06:56 AM

0 Likes
8
3280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 06:56 AM

Citect V6.0 Connection with S7 300 CPU

Dear All,

I have never work with Citect SCADA, and las days i had to convert a PC (where the Citect V6.0 is installed) in Virtual machine.
The SCADA is connected with a SIEMENS PLC S7 315-2DP via Ethernet.

The vistual machine works fine, but the SCADA cannot connect to PLC. I gues there is something in connection settings, But i don´t know where is it.

All computer name and IP address are the same, only the network card name has been changed.
Please help me how to setup the connection between the Citect and PLC.

 

Thank you and best regards.

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2025-01-09 11:43 PM

In response to Mentor
0 Likes
1
2406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 11:43 PM

Hi, You need to add a PC Station in NetPro and set as type Application. Netpro must be installed and running on the Citect IO Server. After you configured the PC Station in Netpro you need to download it as well (same process as downloading to PLC. See attaced screenshot of the fields in NetPro and where they must correspond in the Citect configuration.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2024-07-11 09:25 PM

0 Likes
7
3256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 09:25 PM

Hi, Which driver is the Citect setup to use? PSDirect or S7NT? (To check open Citect Explorer, Change to the Project Editor Menu Communications>IODevices

Reply

Link copied. Please paste this link to share this article on your social media post.

Mentor
Ensign Mentor
Ensign

Posted: ‎2024-07-12 05:33 AM

In response to Hennie_Smith
0 Likes
6
3231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-12 05:33 AM

Hi, Thank you for the comment.

It uses S7NT driver.

Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2024-07-14 10:10 PM

In response to Mentor
0 Likes
5
3204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-14 10:10 PM

The S7NT driver uses the Simatic Net software from Siemens to connect to the PLC. Did you check the Simatic Net is still licensed on the virtual machine and configured?

Reply

Link copied. Please paste this link to share this article on your social media post.

Mentor
Ensign Mentor
Ensign

Posted: ‎2024-07-17 04:35 AM

In response to Hennie_Smith
1 Like
4
3174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-17 04:35 AM

I have check the Simatic PG/PC interface and it is OK.
I can connect the PLC with SIMATIC MANAGER.
Please check the photos of the settings.
Thank you.Screenshot 2024-07-17 114719.pngScreenshot 2024-07-17 114746.pngScreenshot 2024-07-17 114811.pngScreenshot 2024-07-17 114827.pngScreenshot 2024-07-17 114851.pngScreenshot 2024-07-17 114908.pngScreenshot 2024-07-17 115106.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2024-07-17 10:10 PM

In response to Mentor
0 Likes
3
3160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-17 10:10 PM

Hi, All the info above seems correct but need the NetPRO configuration as well to be sure.

Once the configuration is complete in NetPro, it must be transferred to the PC Station. This can either be done by a file or over the Network. Provided that everything is OK, you should see your configuration from NetPro appear in the Station Configuration Editor on the Local PC.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Mentor
Ensign Mentor
Ensign

Posted: ‎2024-12-18 06:57 AM

In response to Hennie_Smith
0 Likes
2
2582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-18 06:57 AM

Dear Hennie,

Thank you for your reply.
Regarding the NetPRO configuration, I am not sure if everything is OK there.
In the Simatic manager, it is configured. Please find a photo of that.Screenshot 2024-12-18 155608.png

Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2025-01-09 11:43 PM

In response to Mentor
0 Likes
1
2407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 11:43 PM

Hi, You need to add a PC Station in NetPro and set as type Application. Netpro must be installed and running on the Citect IO Server. After you configured the PC Station in Netpro you need to download it as well (same process as downloading to PLC. See attaced screenshot of the fields in NetPro and where they must correspond in the Citect configuration.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Mentor
Ensign Mentor
Ensign

Posted: ‎2025-05-20 01:54 AM

In response to Hennie_Smith
0 Likes
0
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-05-20 01:54 AM

Thank you Hennie Smith,

I created an application in the simatic manager and downloaded it, so it created a connection in the simatic net and now it works.

Best regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore