Can ATV630 provide 200% Starting Torque ?
Hello Everyone
I'm working on a project;
This is the description of the customer:
-The VFDs will be used with: Pump, Centrifuge or general purpose.
-The Regulation type: Variable torque
-Drives shall be capable of providing 200% starting torque.
While ATV630 is ideal for pumps and centrifuges, can it provide 200% Starting Torque ?
If not, what's the solution in this case
Thanks in advance for your answers
- Labels:
-
Process Automation Talks
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-03 11:29 PM
If you need 200% overload ATV6xx is in my opinion the false product. Look here.
The drive with the biggest overload is a ATV340 (180% 2s). But If you did not use ATV6xx you will not have dedicated pump functions. For a more detailed analyses I would suggest that you contact your local SE organization to get in contact with a product application specialist for drives.