BMENUA0100.2 time stamping
  • Industrial Automation
  • BMENUA0100.2 time stamping
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Modicon M580
EcoStruxure™ Control Expert
KristianK
KristianK
Cadet
Posted: ‎2024-04-29 10:03 PM
777
Hello all,
I'm trying to make a application where we are reading data from a IEC104 servers with the BMENOR2200 card and transferrers the data AND source time stamp out on a OPC UA server (BMENUA0100.2 card).
It was working, with correct source time stamp and all.
But when I added more signals to the OPCUA server, then the BMENUA0100.2 card started to reboot over and over.
The only way to fix this was to remove the BMENUA0100.2 card from the configuration and load that, and the add the card again with fewer signals.
Ok.. needed to try something; updated CPU firmware 4.10->4.20
Can’t get time stamp to work anymore.
Downgraded CPU firmware 4.20->4.10
Time stamp still not working.
Here is a test of a signal:
SecondSinceEpoch is the same as stamped in IEC104, but value TS is not same.
Signal:
BMENUA0100.2 card:
Test:
SecondSinceEpoch same as IEC104 server
Should TSEventItemsReady be true?
Is there some way to factory reset the OPCUA card, It feels like something is stuck there?
I have tried to set the cyber security rotary switch in reset, but that did not help.
CPU
BMENUA0100.2
BMENOR2200
br
Kristian
  • Smart Design & Engineering
  • BMENUA0100.2
  • OPCUA
Ricard
Lt. Commander Ricard Lt. Commander
Lt. Commander
Posted: ‎2024-05-16 03:47 AM
Hello KristianK
well, where do we start..... from everything you tell me what seems strange to me is the number of variables that after you reduced it started to work . Another one for the #TSEventItemsReady variables that is located zero. It makes me think that some configuration should be reviewed, NTP, Time Zone, daylight, Time Stamping Mode would be "System"
This should be analyzed in depth, contact technical support in your country
Best Regards
Ricard