Aveva System Platform with M340/M580 (EcoStruxure™ Modicon Communication Server vs EcoStruxure™ OPC UA Server Expert)

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Aveva System Platform with M340/M580 (EcoStruxure™ Modicon Communication Server vs EcoStruxure™ OPC UA Server Expert)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Control Expert
product field
Schneider Electric
EcoStruxure™ OPC UA Server Expert
product field
Schneider Electric
EcoStruxure™ Process Expert
field url
Schneider Electric
EcoStruxure™ Control Expert - Modicon Communications Server
field url
AVEVA Group PLC
AVEVA System Platform
Load more

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
dnordenberg1
Lt. Commander dnordenberg1
Lt. Commander

Posted: ‎2025-04-17 05:42 AM

1 Like
6
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-17 05:42 AM

Aveva System Platform with M340/M580 (EcoStruxure™ Modicon Communication Server vs EcoStruxure™ OPC UA Server Expert)

Hi!

We have quite a few modicon controllers and are migrating from a very old third party SCADA to ASP.

We hired a consulting firm that is great at ASP but has almost no experience/knowledge about modicon controllers.

 

Can someone please help me and explain what the practical difference is between these two OPC UA alternatives? They are both listed on OPC UA Server Expert download page, have the same version number so I guess they share significant parts of the code but the download size is way less for Modicon Communication Server (MCS). We downloaded MCS and tested it with ASP and seem to work ok. But why should one chose one or the other? MCS is free but the other is not. Both supports third party OPC UA clients so it is not free because it is "locked to" ASP only. So I can not stop thinking about what MCS might be missing or less good at compared to OPC UA Server Expert?

We also looked at Ecostruxure Control Expert Asset Link but was told it had strict version requirements on ASP so that scared us a bit. I think that route is also better if you start fresh with ASP and modicon controllers, not migrating SCADA and keeping older PLC code, right?

 

And how big really is the benefit of having MCS in Operations Control Management Console instead of in a separate software, I mean it could potentially block you from doing a ASP upgrade if MCS is not updated too or at least verified against the new release or is the Operations Control Management Console integration very version agnostic so it will not be a problem?

 

I see some small pros and cons here but I'm sure I'm missing some larger pieces of the picture here that I can't figure out 😞

 

There is also a third way I'm also a bit curious in but is even more puzzled about and that is the EcoStruxure™ Process Expert for ASP. Pros and cons using that? I see that it is a specialized Control Expert version and we already use Control Expert to manage our controllers today. My feeling is that this is not the best route for us either because of the same reason as Asset Link, we already have all the code done already and that Process Expert would probably have been more beneficial if we started fresh with ASP and modicon controllers, right? I also have slight bad feeling about jumping on specialized software versions unless it gives you some huge benefits that can not be ignored...

 

Kind regards,

David

Labels
  • Labels:
  • Connected Products
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
ciupol
Lt. Commander ciupol
Lt. Commander

Posted: ‎2025-04-17 06:18 AM

2 Likes
4
1636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-17 06:18 AM

I am actually considering my old SCADA to ASP so I have been given multiple presentations (virtual and hands-on) from Schneider including information on your question.

Modicon Communication Server (MCS) is a dedicated solution when you use ASP with Modicon controllers. Ecostruxure OPC UA Server Expert is a OPC UA server for third-party SCADA systems to communicate with Modicon controllers over OPC UA utilizing data dictionary feature.

Since you will be using ASP you definitely want to use MCS. It is free for once (although the price is for sure build into ASP price). I believe it also allows to exchange some extra information between ASP and PLC.

MCS file size is much smaller because as you mentioned MCS is configured through Operations Control Management Console in ASP. Ecostruxure OPC UA have its own configuration interface so that is probably where the additional file size is coming from. Both have the same backbone and both utilize OPC UA for communication.

If possible you also want to utilize Asset Link which gives you a lot of great features for automatic recognition of PLC objects. I also have a lot of old (984 ladder) cade but Asset Link would be great for new development.

Ecostruxure Process Expert is completely different programming environment. It is Schneider's take on DCS (they call it Hybrid DCS). It utilizes Modicon PLCs but programming is completely different than Control Expert.

Reply

Link copied. Please paste this link to share this article on your social media post.

dnordenberg1
Lt. Commander dnordenberg1
Lt. Commander

Posted: ‎2025-04-22 04:26 AM

In response to ciupol
0 Likes
2
1591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-22 04:26 AM

Nice to hear from someone else in the same situation 🙂

You mean using Asset Link in parallell with MCS against the same PLC and use that when doing like new objects which exactly matches ASPs objects?

From what can see Process Expert is Control Expert with a Plant SCADA or ASP integration. So I'm a bit confused about the difference here compared to Asset Link?

Reply

Link copied. Please paste this link to share this article on your social media post.

ciupol
Lt. Commander ciupol
Lt. Commander

Posted: ‎2025-04-23 10:28 AM

In response to dnordenberg1
1 Like
1
1557
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-23 10:28 AM

MCS is only to share data between PLC and SCADA (OPC UA based). Asset Link helps you interpret the data you receive from PLC and automatically objects from PLC and tie them to objects in SCADA. And yes, you run both in parallel. Asset Link is for sure a huge advantage of going with ASP when you have Schneider PLCs. Since you use Schneider PLCs I assume you have some relationship with them so you should ask Schneider to give you some presentations how all this works.

As far as Process Expert goes it is completely different software from Control Expert. Control Expert is based on IEC61131 whereas Process Expert on IEC61499. You can't take logic from Control Expert and use it in Process Expert. You would have to create all the logic in process expert from scratch. Here is a post that describes some of the differences:

https://community.se.com/t5/EcoStruxure-Automation-Expert-IEC/Can-you-tell-me-what-are-the-benefits-...

Reply

Link copied. Please paste this link to share this article on your social media post.

dnordenberg1
Lt. Commander dnordenberg1
Lt. Commander

Posted: ‎2025-04-24 12:26 AM

In response to ciupol
0 Likes
0
1556
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 12:26 AM

Now you mix up Process Expert with Automation Expert hehe. Automation Expert is a whole other thing for sure, we are looking at that for use sometimes in the future but I'm not completely sure if I like the event driven nature of it yet haha.

Yes I do have some Schneider contacts too but they are very sales minded and want to push so hard for Automation Expert all the time and less knowledgeable of other ways forward with currently installed ESCE environment...

Reply

Link copied. Please paste this link to share this article on your social media post.

Sumanjith.an
Sumanjith.an Support
Support

Posted: ‎2025-10-23 12:48 AM . Last Modified: ‎2025-10-23 12:57 AM

2 Likes
0
697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-23 12:48 AM . Last Modified: ‎2025-10-23 12:57 AM

EcoStruxure Control Expert Asset Link:

Asset Link is like a template imported into the IDE and used for integration of control and supervisory systems. Means, it analyses your control project from Process Expert for AVEVA System Platform or EcoStruxure Control Expert and reads the configuration information (Function Blocks), data structures (Variables) and meta data (Comments and Initial Values).By referring to the existing ASP AppObjects, it generates Assets in AVEVA System Platform (ASP), with configured attributes and addresses, reducing engineering time. Once the assets are generated, it can be deployed and make sure the communication with controller is established within no time without any additional efforts. Users can further update control project and same thing can updated in asp side as well with the help of asset link

 

EcoStruxure Process Expert

EPE is a single automation system to engineer, operate and maintain the entire plant.It integrates the Control and Supervision applications to manage the complete life cycle of the applications. EPE delivers values from engineering to operation and maintenance based on Object Oriented configuration with ready-to-use libraries. There are two offers 1.EPE - supervision component is Plant SCADA. 2. EPE for ASP - supervision component is System Platform and both are having control expert as control participant software. Its based IEC61131 and not with IEC61499.

Reply

Link copied. Please paste this link to share this article on your social media post.

EKuznetsov
Lieutenant JG EKuznetsov
Lieutenant JG

Posted: ‎2025-10-27 06:30 AM

In response to ciupol
0 Likes
0
625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-27 06:30 AM

@ciupol 

Hello,

Thanks for detailed explanation.

Just interesting what is your old SCADA and how is replacing to ASP is going?

I saw every video from SE on youtube regarding Asset Link and can't get if it really need this when you have templates, linking of instances to I/O device and mapping  in ASP.  Probably, if you are using GPL in Control Expert and in ASP you get a benefits, but in other cases it is not so obvious? What do you think. Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore