Analog input module quantum Scaling
  • Industrial Automation
  • Analog input module quantum Scaling
Bastian_Schmitz
35
LeTomas
14
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
6
Modicon Quantum
Salah_Mohamed
Ensign Salah_Mohamed Ensign
Ensign
Posted: ‎2022-07-18 06:37 AM
1204
How can I make scaling for analog input module  part no . 140 ACI4000  for quantum PLC ?
  • Connected Products
  • Smart Operations
  • Training
RoozeeR
Lt. Commander
Posted: ‎2022-07-18 08:16 AM . Last Modified: ‎2022-07-18 08:19 AM
There are multiple ways, easiest way you could use the functions from the  EcoStruxure™ Control Expert, I/O Management, Block Library
(also available in Unity-Pro and Concept). See example where the ACI040 is physically located in slot 3:
Example scaling from slot 3 moduleExample scaling from slot 3 module
Other way is create your own DFB, where you have the raw value + Module min/max + Eng values limits +  Offset as input, The scaled value as output. Internally you calculate ScaledValue = RawValue * (ModuleMax- ModuleMin) / (EngMax-EngMin) + Offset.
R.Roozee
Sr Solution Architect (SAE Master)