I have a Altivar 320 and I am trying to set my Relay1 Output to be on when drive is in Run Forward command. I set the I_O parameter according to the manual but when the drive is running the R1 Output is not producing +24V as expected. What am I missing? I want the R1 output to turn on an input on my PLC so that I can write logic to fire a solenoid only when Run Frwd Command is present?????
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-28 11:13 PM
Hi, how do you wire the Relay output? Relay 1 need in your case also 24V+ on the input [R1C] to deliver 24V+ at the output [R1A] . Did you check this FAQ Video
If you connect the +24V from the VSD with the relay and then with the PLC you need to connect COM from the VSD with 24V- of the PLC.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-29 06:43 AM
Hello,
Set R1 to "MFrd".
Also check if the electrical connection is correct.