Altivar 320 Relay output
  • Industrial Automation
  • Altivar 320 Relay output
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Jeremy.Dodd
Jeremy.Dodd
Cadet
Posted: ‎2024-07-25 07:58 AM
727
I have a Altivar 320 and I am trying to set my Relay1 Output to be on when drive is in Run Forward command. I set the I_O parameter according to the manual but when the drive is running the R1 Output is not producing +24V as expected. What am I missing? I want the R1 output to turn on an input on my PLC so that I can write logic to fire a solenoid only when Run Frwd Command is present?????
  • Process Automation Talks
Bastian_Schmitz
Admiral
Posted: ‎2024-07-28 11:13 PM
Hi, how do you wire the Relay output? Relay 1 need in your case also 24V+ on the input [R1C] to deliver 24V+ at the output [R1A] . Did you check this FAQ Video
If you connect the +24V from the VSD with the relay and then with the PLC you need to connect COM from the VSD with 24V- of the PLC.
Kleber
Ensign Kleber
Ensign
Posted: ‎2024-07-29 06:43 AM
Set R1 to "MFrd".
Also check if the electrical connection is correct.