Posted: 2025-01-18 01:11 PM
Hi,
I am currently adjusting our system and would like to be able to display and adjust the current in which the VFD will show a fault through a PLC and HMI.
Is this possible to adjust/view on the ATV320's. My PLC I am using is a M251 with a magelis HMI. I am using ethernet IP communications.
Thanks,
Charlie
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-23 05:07 AM
Good day, I am usually using default mapping in industrial ethernet devices setting.
1. find which parameter You want to control in SoMove on atv320
2. add it to devices scanner, output is for setting from PLC, input is for reading to PLC
3. map correct word to retain variable in PLC, inputs are from atv, outputs are to atv
I hope this is what you were looking for.
Best regards Jan.