Hello Automation Community
I have a VFD: ATV71HC20N4
When I supplied it with Three Ph 400v, it shows : PHF error
We found one open fuse in the input then we short-circuited it by a small wire.
Then we Turned the VFD on again, now it shows NLP error
What are your opinions about how to troubleshoot the issue ?
Thanks for your feedback in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-23 12:29 AM
This is not an issue, it just shows that the drive is waiting for an action on the start command...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-23 03:39 AM
Hello BJAcks
The PHF error was solved , we found an open fuse in the power board , phase one.
Now for the NLP Error, according to the Manual we have to add either a DC Inductance or a Strap between PA/+ and PO.
Link copied. Please paste this link to share this article on your social media post.