Posted: 2025-08-29 05:36 PM
How can I correlate which version of firmware are compatible with one another? I'm having an issue getting the drive to behave with this module installed but there doesn't appear to be a cross reference anywhere within Schneider's public data to tell me which versions are compatible with one another.
For example, I have a v1.17IE04 VW3616 that works fine with this dame drive. But factory defaulting and installing the EtherCAT module causes an SAFF error and the drive won't allow upload /download via SoMove.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-09-08 09:08 AM
Hello.
The ATV320 must be version >= V2.7IE23.
And the VW3A3601 option module must be version >= V1.9IE09.