TM172 Modbus Client - TCP packet count
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM172 Modbus Client - TCP packet count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
Kunal_ch
Kunal_ch
Contributor
Posted: ‎2025-02-03 02:44 PM
1
886
I am using a TM172 PLC as a modbus client and I can count the number of packets coming from the modbus master using sysMODBUS_msg_received_RS485_1 for Modbus RTU.
Is there a similar functionality for TCP? If not, is it coming in the future releases?
  • Connectivity
FedericoM
FedericoM Mentor
Mentor
Posted: ‎2025-02-17 07:26 AM
A similar function is available for BACnet/IP, but not for Modbus/Tcp (it's not planned).
You can use this target block to detect how many client are connected:
FedericoM
FedericoM Mentor
Mentor