Posted: 2023-03-03 05:25 AM
I got a couple of ratiometric pressure sensors which are taking far more current than expected. This means DC 5V is dropping to about 3.6 V (TM172PDG28R)
Besides ditching the sensors and getting new ones´is it possible to use an external power source ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-03 07:08 AM
Maximum current from 5Vout is 50mA.
Being ratiometric, I think you should use the 5V provided by M172.
Input impedance is higher than 20kohm, you should not have this kind of issues...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-03 07:08 AM
Maximum current from 5Vout is 50mA.
Being ratiometric, I think you should use the 5V provided by M172.
Input impedance is higher than 20kohm, you should not have this kind of issues...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-03 07:10 AM
Thanks. Yes, I would say so but wanted to make sure.