Posted: 2025-03-23 12:34 PM
Hi,
I have two questions:
Is it possible to run the BACnet protocol on any of the 2XX series PLCs?
If so, how can this be done?Do any of the HMI panels support BACnet?
Thanks in advance for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-25 11:19 PM
The M2xx controller did not support BACnet. And so far I know the implimentation isn´t planned, because these controllers are Machine controllers and BACnet is a Building fieldbus. We support BACnet with TM172. On HMI site ET6 with Vijeo Designer Basic 2.0 support a little bit BACnet. Normal Vijeo Designer did not support BACnet.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-25 11:19 PM
The M2xx controller did not support BACnet. And so far I know the implimentation isn´t planned, because these controllers are Machine controllers and BACnet is a Building fieldbus. We support BACnet with TM172. On HMI site ET6 with Vijeo Designer Basic 2.0 support a little bit BACnet. Normal Vijeo Designer did not support BACnet.