M172 - Modbus Master

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 - Modbus Master
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
71
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
48
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
geoffrey_tegny_
Crewman geoffrey_tegny_
Crewman

Posted: ‎2020-04-12 02:31 AM . Last Modified: ‎2020-09-10 12:46 AM

0 Likes
10
9584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-04-12 02:31 AM . Last Modified: ‎2020-09-10 12:46 AM

M172 - Modbus Master

Hello guys,

I have some troubles to set up the a TM172PDG42R as Modbus master.

- I set the RS485-2 to Modbus master and the different modbus properties,

- I created a "Generic Modbus" device properly and set its "Modbus address" and "Node number" to 2,

- I added a "FC 03 - Read Holding Register" with a "start address" to 2 and assign the object to a variable created in PLC "Status Variable"

 

But not chance.. The xx flag shows a timeout (at starting) error and I actually cannot see any request message from the PLC with a modbus sniffer.

 

Is there any TVDA available on how to set up a Modicon M172 as Modbus master properly?

Is my RS485-2 com dead?

 

Thank you in advance!

Labels
  • Labels:
  • HVAC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-06-17 11:57 AM

2 Likes
6
9352
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-17 11:57 AM

Hi Geoffrey,

 

to verify whether the RS485-2 is still alive, suggestion is to download an empty project on the PLC (by Download All) and afterwards try to connect to the RS485 port via EcoStruxure Machine Expert HVAC Installer or via Modscan.

 

Please let us know, so that we can eventually follow-up with your enquiry.

 

Have a good day,

Pierpaolo

 

------

Pierpaolo Armeli

Technical Expert Community Facilitator & HVAC Expert

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Rodrigo_Garcia
Commander Rodrigo_Garcia Commander
Commander

Posted: ‎2020-05-05 12:05 PM

0 Likes
0
9470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-05-05 12:05 PM

@AmeliaFaraci 

 

Hello Amelia,

 

Could you take a look to this post?

 

Regards,

 

Rodrigo.-

Rodrigo G. 


Industrial Automation Community manager

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-06-17 11:57 AM

2 Likes
6
9353
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-17 11:57 AM

Hi Geoffrey,

 

to verify whether the RS485-2 is still alive, suggestion is to download an empty project on the PLC (by Download All) and afterwards try to connect to the RS485 port via EcoStruxure Machine Expert HVAC Installer or via Modscan.

 

Please let us know, so that we can eventually follow-up with your enquiry.

 

Have a good day,

Pierpaolo

 

------

Pierpaolo Armeli

Technical Expert Community Facilitator & HVAC Expert

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2020-06-18 12:54 AM

0 Likes
1
9335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-18 12:54 AM

 

vOKandFALSE.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffrey_tegny_
Crewman geoffrey_tegny_
Crewman

Posted: ‎2020-06-19 05:08 PM

In response to Anonymous user
0 Likes
1
9308
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-19 05:08 PM

Hello Pierpaolo,

 

Thanks for your help.

I actually "fixed" my issue by sending the code again and again to my controller.. I had to set up 19 controllers and had to send again when the communication were not working properly. I don't know if I were no patient enough or send it again fixed the problem.

But now everything is fine.

Thank you!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

geoffrey_tegny_
Crewman geoffrey_tegny_
Crewman

Posted: ‎2020-06-19 05:09 PM

In response to ismailozinan
1 Like
0
9305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-19 05:09 PM

Good tips.

thanks "ismailozinan"

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-23 02:41 AM

In response to Anonymous user
0 Likes
3
8142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 02:41 AM

I am using M172PDG42R and have an issue with RS 485 communication. I have done all possible requirement for which I should get Data from PLC through RS 485 (2) port. I am not able to get value in modscan software. Please guide. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-03-23 03:02 AM

In response to geoffrey_tegny_
0 Likes
0
8139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 03:02 AM

Please guide me . I am facing issue for Modbus communication of M172 PDG42R RS485

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-23 03:04 AM

In response to Anonymous user
0 Likes
0
8137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 03:04 AM

Did you have problems to read values or to write values or booth in the case the TM172P is the modbus master? Please check the serial line parameters which you configure via configuration. These parameters will be used after a download all via CONNEC.PAR. The parameters which you can enter via BIOS Parameter or Commisioning will be over writter from the configuration of Modbus Master in configuration. Did you check the status of your slave like explained in the former posts?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Lt. Commander ismailozinan Lt. Commander
Lt. Commander

Posted: ‎2021-03-23 03:22 AM . Last Modified: ‎2021-03-23 06:45 AM

In response to Anonymous user
0 Likes
1
8134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 03:22 AM . Last Modified: ‎2021-03-23 06:45 AM

Hello,

if you are using modbus scan software.Modbus scan software is master. In this case TM172 should be as a slave

Please check step by step at  below lines. After that you can not take a response from TM172, could you plase connect to TM172 via micro USB cable or ethernet for check modbus parameters of RS485-2 via commisioning tab.

BR

 

 

stp1.jpg

 

stp2.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-23 03:26 AM

In response to ismailozinan
1 Like
0
8131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-23 03:26 AM

As additional information. If you use RS485-2 as slave a change of communicaiton paramters (Baudrate;Parity...) need all time a restart of the controller. To restart the controller remove the power supply and the Mini USB cable. Did you get a response or a error code from modscan?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of