GREETINGS
M172 PLC
I NEED TO MOVE DIFFERENT VALUES
IN THE PLC
OTHER THAN THE VALUE TO BE WRITTEN FROM HMI TO THE EEPROM VARIABLE
BUT I GET AN ERROR I CANNOT MOVE I WOULD BE HAPPY IF YOU CAN HELP
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-26 05:08 AM
Hello,
if you want to assign a value to an EEprom variable you have to use the target functions:
sysWritePar<type>()
e.g.:
sysWriteParReal(ADR(eepromRealVar),rNewValue);
These functions make an internal check to verify if the newValue is different from the one currently stored in order to perform an EEprom update only when it is really necessary
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-26 05:08 AM
Hello,
if you want to assign a value to an EEprom variable you have to use the target functions:
sysWritePar<type>()
e.g.:
sysWriteParReal(ADR(eepromRealVar),rNewValue);
These functions make an internal check to verify if the newValue is different from the one currently stored in order to perform an EEprom update only when it is really necessary
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-01 10:22 PM
You have to add to the adress input the FC ADR. It should look like this
Link copied. Please paste this link to share this article on your social media post.