Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-09 03:10 PM
Hi,
I have a setup with the TM172PDG42RI and two TM172E28R connected on the CAN expansion bus. I was wondering if there is a system variable on the controller to "restart" the CAN communication. What I am experiencing is that if I have the controller started up first before starting up the expansion modules, the controller would not communicate with the expansion module. The controller would need to be reboot to re-establish the communication.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 09:52 PM
Hi , so far I knwo there is at the moment not a target variable to restart the CAN communication. During the bootup the PLC will send a start Signal to all Slave devices in the network. If the Expansion starts later like you described it will not work.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 09:52 PM
Hi , so far I knwo there is at the moment not a target variable to restart the CAN communication. During the bootup the PLC will send a start Signal to all Slave devices in the network. If the Expansion starts later like you described it will not work.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-07-10 11:11 PM
Hi,
this option is available on TM173O with target block:
sysCopm_Reboot(COPM_CHN_ENUM#COPM_CHN_CAN0)
On TM172 the only option is trigger a PLC reboot from background task: