Posted: 2024-11-16 01:31 PM
Hello
I have a TM172PDG28RI controller and a TM172DGRP monochrome panel
The TM172DGRP panel has three leds
Question:
How to make the leds on the TM172DGRP panel reflect those on the TM172PDG28RI controller (red/yellow/green)
I assumed that this was done automatically after setting up communication, but the LEDs did not light up.
I have the same configuration for the display on the controller and remote panel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-17 11:02 PM
You need to control the LED via Display part. You could find a sample for this in the integrated TVDAs Chiller Large/ AHU Large.
You need to create a Global Procedure to activate the LEDs.
And you need to read the status for the LED mostly via Video_GetParam function.
You could find here the TVDAs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-17 11:02 PM
You need to control the LED via Display part. You could find a sample for this in the integrated TVDAs Chiller Large/ AHU Large.
You need to create a Global Procedure to activate the LEDs.
And you need to read the status for the LED mostly via Video_GetParam function.
You could find here the TVDAs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-19 08:45 AM
Thank you Bastian for your help
I can control LEDs on the operator screen turn off and on the LEDs by manually entering the values in the variable:usiLEDsCPU: USINT Array (0...2)
I have a problem with the GetParam function. I entered in GlobalOnTimer:
uiRET := Video_GetParam( 0, sysLocalLeds, 0, usiLEDsCPU, tyUSInt);
sysLocalLeds:= usiLEDsCPU;
There is no error during download, but the LEDs on the panel do not work.
Can you write what I did wrong?
I am a beginner in programming Medicon controllers. I work mainly with Siemens controllers and the TIA portal program.What is very simple in Scheider Electric is difficult and vice versa 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-25 06:51 AM
You need to specify the modbus Register of sysLocalLeds in the function Video_getParam. In the TVDA all variabels which are written in UPPERCASE are constanst for the register adress. In you case you need to enter as adress 8640 LED1 8641 LED2 8642 LED.
Link copied. Please paste this link to share this article on your social media post.