Fan management - variable speed and fixed speed fans
HVAC and Pumping Forum
Select a Country
  • Industrial Automation
  • HVAC and Pumping Forum
  • Fan management - variable speed and fixed speed fans
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
otrotabi
otrotabi
Contributor
Posted: ‎2025-05-16 03:58 AM
840
When using compressor racks with both variable speed and fixed speed compressors - which is the most used scenario-  the CompMgmtVS FB has the built in logic to handle this setup.
A similar setup is used also for condensing pressure control, meaning that there typically are some fixed speed ON-OFF fans and variable speed fans. However this does not seem to be covered by FanMgmt FB which, as far as I understand, seems to assume every fan is a variable speed fan.
So, two questions: 1) Is my understanding correct, or by properly configuring some inputs the FB while handle this and 2) in case I am right, is there another FB I could use for this setup.
I need to control a very simple chiller with one EBM EC fan and one AC fan.
  • HVAC
  • ecostruxure
  • hvac
  • TM171
  • TM172
FedericoM
FedericoM Mentor
Mentor
Posted: ‎2025-05-19 01:04 AM
FanMgmt assumes that in case the VSD is present, all the on Fans are driven at the same frequency.
If you want to drive fans like compressors, I think you can reuse the CompMgmtVS even for fans.
You can reuse also the CompCntrl_VS or generate the value of usiStatusC1-C2 based on the Fan required and the related alarm status.
Other useful blocks are:
- EcFanMgmt under Application-->Air library
- EBM modbus blocks under Communication-->EBMpapstModbusCom library
FedericoM
FedericoM Mentor
Mentor